so what's the load????? if you apply diversity, you could probably use 6mm single circuit for both. that would cut the cost.
 
Right i'm going to feel a right knob now but if you don't ask you don't learn and all that what's diversity? how do I use it, and where can I find all this info from guys, except the regs of course websites and such, yep I feel like a knob already lol
 
Right i'm going to feel a right knob now but if you don't ask you don't learn and all that what's diversity? how do I use it, and where can I find all this info from guys, except the regs of course websites and such, yep I feel like a knob already lol

In the OSG
 
Tables for diversity can be found in Appendix 1 of the On Site Guide.
For cooker appliances, it is 10A plus 30% of full load where the full load is above 10A.
As you appliances would have a combined full load of abot 27A, that would be 10A + 30% of 27A (8.1A) a total of 18.1A.
4mm² has a current carrying capacity of between 17.5A to 37A, depending on Reference Method.
From what you have said, the capacity is going to be at or near the maximum.
 
Thanks guys. I love this site so many informative people. Just to explain i've recently come back to install from a maintenance job where 17th edition and health and safety was seen as a way of getting out of work (they actually said this), please be patient whilst I'm getting used to the laws and standards again, many thanks.:cool:
 

Reply to 30A induction hob and 30A oven in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
155
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
522
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
465

Similar threads

  • Question
In all likelehood, no different. The RCD on the left is looking for electricity that is going missing in action. If the total missing reached...
Replies
3
Views
1K
  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
676

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top