30kw boiler cable calculations | on ElectriciansForums
Discuss 30kw boiler cable calculations in the UK Electrical Forum area at ElectriciansForums.net
M
meggerlover
Hi guys just a quick check in my calculations for a quote I'm doing
15meters clipped direct
30,000w divided by 400v
= 75a per phase
im using sy cable and think 16mm 5 core is best
What you guys think
Just about every bit of kit I've ever fitted like this has had a plate on it which gives information about what it should be connected to. These can be interpreted as manufacturer's instructions and should (most likely) be taken into consideration.
Does this boiler have one?
Pah, who needs an info plate when you're as knowledgeable as the OP?!
That SY is bugging me more than the blunder of thinking that just splitting the power rating by three gives you phase current!
There's a smorgasbord of cable choices and containment options available to the OP, 99% of them more suitable than SY!?
Reply to 30kw boiler cable calculations in the UK Electrical Forum area at ElectriciansForums.net
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...