30ma rcd tripping after replacing consumer unit | on ElectriciansForums

Discuss 30ma rcd tripping after replacing consumer unit in the UK Electrical Forum area at ElectriciansForums.net

muzza1

-
Joined
Feb 21, 2013
Messages
85
Reaction score
14
Location
london
Hello all, how are you?
I often look on here but the time has come to ask for some advice!
Nearly finished some alterations in a customers Kithen, Dining room, Utility room and Garage. Approx 3 days work in total.
Anyway, after all 2nd fixed and new split load board installed pop goes the rcd! Proper annoying!
It was found that when the ch+hw boiler was switched on at the spur it tripped the 30ma rcd on the split load board, here we go, i thought :sad:
Explained to the customer the situation and after bypassing the rcd hopped in the van knowing Monday is going to be a headache, (can't stand fault finding!)
To try and cut a long story short, i was after some advice or ideas re how to get round this problem without some testing deep within the customers boiler etc with certification and notification in mind!

I hope i've made some sort of sense with my question!

Thanks for any help on this chaps.
 
Hello all, how are you?
I often look on here but the time has come to ask for some advice!
Nearly finished some alterations in a customers Kithen, Dining room, Utility room and Garage. Approx 3 days work in total.
Anyway, after all 2nd fixed and new split load board installed pop goes the rcd! Proper annoying!
It was found that when the ch+hw boiler was switched on at the spur it tripped the 30ma rcd on the split load board, here we go, i thought :sad:
Explained to the customer the situation and after bypassing the rcd hopped in the van knowing Monday is going to be a headache, (can't stand fault finding!)
To try and cut a long story short, i was after some advice or ideas re how to get round this problem without some testing deep within the customers boiler etc with certification and notification in mind!

I hope i've made some sort of sense with my question!

Thanks for any help on this chaps.

Did you do any testing at all on your work before energising or just switch on and hope for the best ?
 
How exactly did you bypass the RCD?

There's hardly a lot of fault finding to be done is there, you already know it's in the boiler controls somewhere. It's hardly going to take you long to go through a domestic boiler circuit, is it a combi or heat only boiler?
If the fault proves to be internal to the boiler you'll be looking at getting a plumber out to fix it, and if you didn't have the sense to add a suitable disclaimer to the quote/contract then you might be paying for it.
 
i would disconnect heating system at fused spur, test up to that point prove all results, then speak with client about a fault on the heating system should the fault be after the fused spur. should it be on the supply up to fused spur then sort it out with them.

heating system if not a combi

disconnect boiler
disconnect pump wiring if not in boiler
IR test pump to earth
If pump IR test 0M ohms or there about's faulty pump
remove programmer cover bridge out L to no 3 & 4
turn up thermostat & cylinder Stat
IR test on secondary of the fused spur that you disconnected (boiler still not on circuit)
LN-E see if you have 0M ohms or close to it or clear
then open valve manually
same IR test
should show all the way to boiler.
if all clear above then put back together & would probably tell you that fault is in the boiler.

the above is for 230V controls & not low volt.
should you have a system's boiler you can probably unplug the pump & test it inside the boiler.

if you can't understand any of the above you are probably out of your depth & should consult your client to get someone in who can fault find on an electrical system.
the above is a basic heating system layout & may not cover every variation but it is a start for you.
good luck
 
Last edited:
Didn't do any testing prior to working on the ring main, getting complacent.
The original wiring is only approx 15 years old and not been messed about with so took it for granted that i shouldn't come across any problems.
After replacing board and identifying fault just supplied the ring from the 1st way next to the main switch, non rcd protected.
(Obviously i realise this can't be more than temporary)
To be honest i think i need to take a step back at the beginning of each job from now on and concentrate on doing some testing before getting the tools out and just cracking on! There's no way i can sign this job off until boiler fault is sorted, but as this spur is back to back with the cu any ideas on possibly feeding spur via 5amp radial non rcd protected from board.
It's a standard fully pumped ch system with 3 port etc.
I'll get cracking on with testing as much of the heating system as i can and hopefully will be able to crack it without calling a Boiler engineer, looks like being an interesting Monday morning!
 
You could possibly feed the boiler circuit from a non RCD circuit if certain criteria are met BUT that isn't an alternative to methodically finding and rectifying the fault. Check through the wiring associated with the boiler and controls and take nothing for granted - but also carry out the full testing on the ring just to make sure nothing is fooling you.
 

Reply to 30ma rcd tripping after replacing consumer unit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
860
Ok I’ll try this when I’m down
Replies
4
Views
385

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top