Hello all, how are you?
I often look on here but the time has come to ask for some advice!
Nearly finished some alterations in a customers Kithen, Dining room, Utility room and Garage. Approx 3 days work in total.
Anyway, after all 2nd fixed and new split load board installed pop goes the rcd! Proper annoying!
It was found that when the ch+hw boiler was switched on at the spur it tripped the 30ma rcd on the split load board, here we go, i thought :sad:
Explained to the customer the situation and after bypassing the rcd hopped in the van knowing Monday is going to be a headache, (can't stand fault finding!)
To try and cut a long story short, i was after some advice or ideas re how to get round this problem without some testing deep within the customers boiler etc with certification and notification in mind!

I hope i've made some sort of sense with my question!

Thanks for any help on this chaps.
 
Makes sense Dave.
Does anyone enjoy fault finding?

I love it Muzza, you get to become a bit of a detective and have to start a logical process of elimination. However, I would not enjoy if I was under pressure so I try and plan and make time for the fault finding.
 
I'll try and make it theraputic next time i'm testing!

I'll let you know how i got on.

That would be very interesting Muzza, you tend to get more help on this site if you become a bit more interactive.
 
I love it Muzza, you get to become a bit of a detective and have to start a logical process of elimination. However, I would not enjoy if I was under pressure so I try and plan and make time for the fault finding.

Me too, the satisfaction you get when you have tracked down that elusive neutral earth fault and you test the cable again and it's all good and then flick on the RCD and it holds. You think glass of wine when I get home to celebrate.

Then you go home really chuffed at fixing it and tell the Missus and go into massive detail about what the problem was and all she can say is "oh right"! Then the bubble is burst and your back to reality.:wink_smile:
 
haha, i know that feeling well!
Me too, the satisfaction you get when you have tracked down that elusive neutral earth fault and you test the cable again and it's all good and then flick on the RCD and it holds. You think glass of wine when I get home to celebrate.

Then you go home really chuffed at fixing it and tell the Missus and go into massive detail about what the problem was and all she can say is "oh right"! Then the bubble is burst and your back to reality.:wink_smile:
 

Reply to 30ma rcd tripping after replacing consumer unit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
852

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
860
Ok I’ll try this when I’m down
Replies
4
Views
386

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top