View the thread, titled "32 Amp Cooker Circuit 13 Amp Cooker" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.
Hi,thanks for replying.The Beko Ceramic Hob is 32Amp/6.7Kw and cooker oven is fitted with a plug which I believe was installed when the kitchen was up graded by Magnets for the previous owners few years back. I was wondering if the 32Amp circuit will manage both loads without tripping the system. As mentioned earlier the circuit is a dedicated 32Amp for the cooker. Many thanks.
Hi do you know the rating of oven ,although it has a 13 amp plug it may be less than that .there will be a sticker on inside of oven door usually. Is your cooker switch with socket in a unit adjacent to oven
On the face of it, the Hob could use the entire capacity of the 32A circuit, so without further info the immediate response is - no, don't connect the oven to that circuit as well.
Knowing a bit more about the requirements of the oven, as above, would be useful.
The reality is that if you don't normally use the full capacity of the hob, then having the oven on that circuit would probably not normally trip the breaker. The old chestnut everybody quotes is .... when Christmas dinner is in the oven and lots of pans on the hob etc etc that's the one time it trips!
The hob is rated at 32A and the oven will have a maximum load of 13A, although most probably less, so a total of 45A.
In my book, a hob over an oven can be considered as a 'cooker', and there is a diversity calculation allowed for these.
The formula is 10A + 30% of the remainder + 5A if a 13A socket is present on the cooker isolator.
10 + 30% of (45-10) + 5A = 10 + 10,5 + 5A = 25.5A, so well within the capacity of a 32A circuit.
Hi, I've checked and the oven is rated as 2.8Kw and the new Beko Hob is rated as 6.7Kw. The cooker switch socket is located in the unit adjacent to the cooker. I hope this helps. Thanks and Regards.
So as brianmoooore says, diversity (wot I didn't consider!) makes it fine. Ignore my post #17 and go ahead as you originally suggested. It sounds fine!
Thanks very much guys for all your input, i'll go ahead now and replace the gas hob with the Beko Ceramic. One thing I have noticed and that is during the previous upgrade they had changed the cooker switch to a double switched socket to accommodate plug for the cooker and the plug for the gas hob spark igniter, is this the norm. Once again many thanks to all. Regards
Ive started fitting these now, i dont love the 13amp fuse behind the appliance but rarely blow unless there is an issue and only 2 screws to access.
Could mount in cupboard adjacent but no good if its drawers
Reply to the thread, titled "32 Amp Cooker Circuit 13 Amp Cooker" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.
markthespark,
bigspark17,