Hi all
I know that ovens have to have own supply over 2kw
I have a question on a electric oven and gas hob with ignitor on 0.75 flex so i thought 16A breaker to a 20amp dp switch and double socket but after having a look at the job and oven i found wattage of oven was 3250watt so draws 14.13amp

I am now thinking 2.5mm t/e cable, 16amp breaker, 20amp dp switch and flex outlet the oven is not wired with a flex but manual says three core 1.5mm Hov5 V-F flex, also need a socket for the ignition of gas hob which i may now do off a sw/f/spur to low level socket is this ok any advice please chaps or suggestions of a better way
 
Hi all
I know that ovens have to have own supply over 2kw
I have a question on a electric oven and gas hob with ignitor on 0.75 flex so i thought 16A breaker to a 20amp dp switch and double socket but after having a look at the job and oven i found wattage of oven was 3250watt so draws 14.13amp

I am now thinking 2.5mm t/e cable, 16amp breaker, 20amp dp switch and flex outlet the oven is not wired with a flex but manual says three core 1.5mm Hov5 V-F flex, also need a socket for the ignition of gas hob which i may now do off a sw/f/spur to low level socket is this ok any advice please chaps or suggestions of a better way
Did you get me PM mate?
 
Haven't got any tables in front of me but i would be tempted to go bigger again, so as to future proof it, so that at a later date the people can put an electric hob in or bigger oven. Much easier to do it now than later, bigger cable also reduces the chances of volt drop problems (depending on run length)
 
Haven't got any tables in front of me but i would be tempted to go bigger again, so as to future proof it, so that at a later date the people can put an electric hob in or bigger oven. Much easier to do it now than later, bigger cable also reduces the chances of volt drop problems (depending on run length)
length of run only about 10metres or less
so how would you do this as they are only doing it to sell house so cost of renewing again someone elses problem
It has a free standing gas cooker at minute its the mother in laws house and trying to keep costs down
It does not have a cooker circuit at the minute and brother in law fitting new housing for single oven
i need a supply for 3250kw oven and the ignitor for the gas hob
would it be acceptable with 16amp breaker 2.5mm cable and a 20amp dp to a double socket or should i
go with a flex outlet with ignitor on a single socket from a fused spur
 
Last edited:
If they are doing it just to sell the house and money is tight then not so much point in my future proof suggestion :eek:. Be aware though that a new circuit into a kitchen is notifiable so people may well want to see all the correct paper work when the sale goes through. Depending on installation method you might not even need a fused spur for the igniter as "clipped direct" for 2.5mm gives you 27 amps.

BTW no problem with VD on such a short run.
 
cheers mate
yeah volt drop i checked so i am ok to just use double socket off 16a 2.5mm cable and 20amp dp switch and using method c clipped direct and there is a spare way on protected side of mains as its only got split load board with 1 30ma rcd 100amp
is the 1.5mm flex ok as manual states 1.5mm Ho5v v-f i am guessig but is this just heat resistant flex
 
Last edited:
cheers mate
yeah volt drop i checked so i am ok to just use double socket off 16a 2.5mm cable and 20amp dp switch and using method c clipped direct and there is a spare way on protected side of mains as its only got split load board with 1 30ma rcd 100amp
is the 1.5mm flex ok as manual states 1.5mm Ho5v v-f i am guessig but is this just heat resistant flex

can't see any probs with what you are suggesting although i think i would put in just a single socket rather than a double for the igniter so people don't start plugging in tumble dryers at a later date (you could even use a 5A round pin plug and socket to ensure it stays dedicated to the igniter)
Also a 20A mcb would give a little more flexibility.

Does the oven come with a flex? Using heatproof flex can't do any harm but i would have thought that the oven would be designed with enough insulation so as not to need it - but check the manual for what it says.
 
can't see any probs with what you are suggesting although i think i would put in just a single socket rather than a double for the igniter so people don't start plugging in tumble dryers at a later date (you could even use a 5A round pin plug and socket to ensure it stays dedicated to the igniter)
Also a 20A mcb would give a little more flexibility.

Does the oven come with a flex? Using heatproof flex can't do any harm but i would have thought that the oven would be designed with enough insulation so as not to need it - but check the manual for what it says.
no it doesnt come with a flex it just says use 1.5mm ho5v v-f flex whatever that is and also thought of using 20 amp breaker its a mem type db with a bs 4293 rcd 100a and type b ab16sb 16a breaker if i can still get one or ab20sb 20a type b
so should i use a flex outlet for oven and do the single socket of the ring for ignitor with fused spur as there are two flexes one for the oven and one for ignitor
 
no it doesnt come with a flex it just says use 1.5mm ho5v v-f flex whatever that is and also thought of using 20 amp breaker its a mem type db with a bs 4293 rcd 100a and type b ab16sb 16a breaker if i can still get one or ab20sb 20a type b
so should i use a flex outlet for oven and do the single socket of the ring for ignitor with fused spur as there are two flexes one for the oven and one for ignitor

SEC-tom's link just says its ordinary flex as it is rated up to 70C .

If the ring is close you could put it on that or no reason why you can't spur it off the cooker radial - there is enough spare in the cable from what you have said - either way is fine as far as i can see.
 
SEC-tom's link just says its ordinary flex as it is rated up to 70C .

If the ring is close you could put it on that or no reason why you can't spur it off the cooker radial - there is enough spare in the cable from what you have said - either way is fine as far as i can see.
so is it ok to run a 2.5mm from 20dp to flex outlet and then a 2.5mm of the same switch for single socket
 
mother in law
this is all she wants as she is selling house
so as i have the 2.5mm and not charging the costs kept to a minimum if it was upto me i would run 6mm for cooker and a seperate circuit for oven but this is all she wants i need a supply for a 3250w oven and the ignitor for the gas hob whats best way mate is it ok to run 1x 2.5 mm to 20 dp switch and then two separate 2.5mm from that one for flex outlet to oven and 1 for single socket for ignitor as pushrod says if i put a double socet it may be overloaded by someone in future
 

Reply to 3250watt oven in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
162
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
580
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
495

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top