Hi all
I know that ovens have to have own supply over 2kw
I have a question on a electric oven and gas hob with ignitor on 0.75 flex so i thought 16A breaker to a 20amp dp switch and double socket but after having a look at the job and oven i found wattage of oven was 3250watt so draws 14.13amp

I am now thinking 2.5mm t/e cable, 16amp breaker, 20amp dp switch and flex outlet the oven is not wired with a flex but manual says three core 1.5mm Hov5 V-F flex, also need a socket for the ignition of gas hob which i may now do off a sw/f/spur to low level socket is this ok any advice please chaps or suggestions of a better way
 
thanks guys
Think i will stick to16 0r 20 amp breaker 2.5mm with 20a dp switch to flex outlet and either spur single socket off this or just put a fused spur of the ring
as i have to put a fused spur for extractor hood also
if i was to future proof would it be ok to wire in 6mm to 45amp cooker sw with a cooker outlet and connect the flex to this with a 20 amp breaker would this be acceptable
dont want to put a 32 or 40amp breaker as this is way above what i need and would take a lot of fault current to trip breaker in the event of fault?
cheers guys
 
I would never wire it in 2.5

You gotta think of the next owners of the property mate, probably electrically clueless. They could fit a range cooker and not even know that an upgrade is needed to the circuit.
 
probably will do it this way will have to see what mother-in-law and her son as he sorting kitchen either way its up to them
i just thought as 2.5mm has enough current carrying capacity ad satisfies volt drop i would leave the cooker circuit for new owners to do but will see
 
Hi guys just thought i would update you on the above
I went round to carry out a visual ispection befor doing above and have a couple of questions if ok

Its a TN-S system, has a MEMERA 2000 ccu with only 1 side RCD protected by a 30mA 100amp RCD
there is a type 1 and b mixed breakers 40amp type b bsen60898 for shower, 32amp type 1 bs2871 for ring circuit but also discovered two radials for in 2.5mm for 1 socket in kitchen and another radial for a single supplying fridge and then onto double in front room for TV,VCR, DIGI BOX AND DVD, 16amp for a fused spur for heating controls only on RCD protected side and 1 spare way which i am thinking of using for Oven circuit

Then on unprotected side of CCU there is a mem type 1 32amp with a radial in 2.5mm supplying double for socket in attached outbuilding for a freezer in a brick shed
then there is a 6 amp type 1 supplying whole house for the lighting in 1.0mm and also a 1.0mm supplying a bulk head light in alley way and onto another in the shed all udercover from the elements

The main earthing conductor is in 6mm it looks and is connected to a old style MET with BOLTS not very well as some of strands hanging out how do i work out by calculation if this is satisfactory do i DO I divide 230v by Ze to get the fault current and then do adibiatic equation ????
and will i need to upgrade it to 16mm if i install new circuit for oven

ther is NO water bond that i can see but not deffo LOOKS as if there is a 6mm going to bathroom need to check
GAS bond also in 6mm
most of sockets to kitchen are spurred of ring I think
IT looks like i will be better doing a periodic first as there may be other things

would it be ok to add these radial sockets into the ring rather than having one ring circuit and two radials as at the minute the radials are being protected by a 32amp breaker for ring and so exceeding current carrying capacity of the 2.5mm t/e
also will i have to install RCD or RCBOs for the lights and the socket radial in shed as well as replacing the 32amp cb for 20amp cb or RCBO

and a quick press of theBS4293 100a 30ma RCD and you guessed nothing so looks knacked and will need replacement any ideas if possible to get one
is it possible to get replacement cbs for MEM2000 ccu is it eaton who supply replacements any advice with any of above would be very helpful cheers sorry its a long post chaps
 
Last edited:

Reply to 3250watt oven in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
162
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
580
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
495

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top