Quickie - Would you say this is ok?

32A MCB feeding 6mm T&E which is then connected to a 2.5mm T&E & 1.5mm T&E cable via a 30A terminal block in plastic terminal block housing buried in stud wall.
The 2.5mm feeds a 3kW immersion heater with 13A SFU at the heater end.
The 1.5mm feeds gas boiler with 13A SFU at the boiler end.

Initially I thought the 1.5mm cable should not be fed with a 32A fuse but thinking about it - fault protection is provided by the 32A MCB & overload protection is provided by the 13A SFU at the end of the circuit rather than the beginning. Just doesn't seem good practice to feed a 1.5 & 2.5mm cable from a single 6mm cable protected by 32A but is it ok?

Not ideal to have boiler & water heater fed off same supply.

Fuse in switched fused spur to water heater is on the limiter - non fused switched unit would be better?

Connection should be maintenance free.

Should the connection be rated for design current or be equal to or greater than the fuse (in this case 32A)?

Many Thanks

Chris
 
Not sure why you are disagreeing, Zs is measured at the furthest point at the supply terminals of the fcus.
Yes sorry that's absolutely right but not relevant to the point, i was explaining about the"Z" at the point relevant to the adiabatic, of course you were right to correct me on my incorrect use of the term Zs. Sorry for confusing matters!
I have changed to creative as there's no button for "yes agree, but that's not the point in question"
 

Reply to 32A MCB feeding 1.5mm & 2.5mm T&E cables via 30A terminal block in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
223
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
683
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
625

Similar threads

  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top