Hi there,

I have been asked to install a 32a supply for a hot tub for a client. I haven’t installed a supply for a hot tub before and having done a bit of research I am getting mixed answers about doing this on a PME system. I have a DB under the stairs with plenty of spare ways so I would be planning to take a 6mm armour from here outside to a rotary isolator. what I am unsure about is the earthing scenario, I have seen a lot of people saying this will require an earth rod. There is also the possibility of taking tails directly of the Henley blocks into a small garage unit and feeding the hot tub of its own DB. Any help is greatly appreciated thanks in advance.
 
I still don’t see the insistence of installing an electrode to an all insulated glorified paddling pool, so your In the water and step onto the grass??
Surely they would be included in part 7 if special supplementary requirements need to be considered ( I don’t consider them to fall into 702, if they did they’d be in there)
 
If you go back and read the regs again you will see that the >20ohm earth electrode is a note and that they do allow a hottub to be connected to a supply fed by PME without it.
Ah I read it that it was a requirement but will have another look, just as an aside, the manufacturers of 3 out of the 4 I have installed in the last month have said they must have an electrode, 1 said the opposite. I'll look back in regs in a bit
 
Ah I read it that it was a requirement but will have another look, just as an aside, the manufacturers of 3 out of the 4 I have installed in the last month have said they must have an electrode, 1 said the opposite. I'll look back in regs in a bit

I might be wrong, I haven't actually looked at it since the change to the 18th edition but it always used to be a note at the end of a regulation saying that you could install an earth electrode with Ra <20ohms connected to the equipotential bonding system of the installation.

A key point on this for me is that it says 'connected to the equipotential bonding system' not to create a seperate TT earthing system or anything like that. As far as I am concerned this means an earth electrode system connected to the MET of the installation.
 
Our favourite word "reccomend" makes an appearance.....
 

Attachments

  • [ElectriciansForums.net] 32a supply for a hot tub of a PME supply.
    20200626_103002.jpg
    44.2 KB · Views: 47
If you go back and read the regs again you will see that the >20ohm earth electrode is a note and that they do allow a hottub to be connected to a supply fed by PME without it.


And the key here is if you can’t get 20ohms - which you won’t with an normal earth rod in majority of cases, then don’t install one .

Remember the regs are a guide not statutory .
 
And the key here is if you can’t get 20ohms - which you won’t with an normal earth rod in majority of cases, then don’t install one .

Remember the regs are a guide not statutory .
But part p a statutory document requires that the installation complies to bs7671 which gives a reason to follow it.
 
And the key here is if you can’t get 20ohms - which you won’t with an normal earth rod in majority of cases, then don’t install one .

Remember the regs are a guide not statutory .

What would you class as a 'normal' earth rod?

I have installed many earth electrodes, made up of multiple standard rods, with Ra of less than 20 ohms.

Plus of course there are the many lightning protection installations which use standard rods to achieve even lower values.
[automerge]1593207517[/automerge]
Our favourite word "reccomend" makes an appearance.....

I think that has changed, it now states supplementary equipotential bonding whereas I am sure it used to just say equipotential bonding.
To my mind this possibly moves the intended point of connection of the earth electrode to be local to the swimming pool or other basin.
 
...I think that has changed, it now states supplementary equipotential bonding whereas I am sure it used to just say equipotential bonding.
To my mind this possibly moves the intended point of connection of the earth electrode to be local to the swimming pool or other basin.

Yes was just looking at 702 again and actually states where you are USING PME earth as the supply to the "basin" then it recommends the electrode is added to the supplementary bonding :
"NOTE: Where a PME earthing facility is used as the means of earthing for the electrical installation of a swimming
pool or other basin, it is recommended that an earth mat or earth electrode of suitably low resistance,"


So it states the opposite of the lengths most prescribe of isolating the PME earth from the hot tub supply using stuffing glands, cutting back the armour etc, you just could/should add an electrode in the ground and bond it loacally at the sub board or close by...


ps I'm still unsure the logic/reason for seperating the PME earth from a "TT"'d installation for eaxample to an outbuilding when you could equipotentially bond it back or via a marshalling terminal to the PME earth ? (providing you have the correct size bonding conductor)
 
ps I'm still unsure the logic/reason for separating the PME earth from a "TT"'d installation for example to an outbuilding when you could equipotentially bond it back or via a marshalling terminal to the PME earth ? (providing you have the correct size bonding conductor)
The usual reason for TT-ing an out building is the 10mm size of the CPC if it needs bonding to extraneous conductive parts in the out building from a PME-derived supply.

If you are feeding via 10mm or more SWA (with a CPC, or armour of equivalent rating) no issue, but if its a 4mm run then you either need a supplementary CPC or simply isolate it via a TT-ing RCD device and use a local earth rod.

As for the earth mat/rod for an outdoor pool it makes sense. The issue for safety is the voltage difference between the water/metal in the event of a PME fault, and the Earth around the pool. Even if the earth rod/mat is unable to pull the PME fault down close to true 0V, it will still raise the surrounding soil to (hopefully) a small enough difference in potential for anyone stepping out of the pool.
 
Here it’s an older copy mind View attachment 59055
Should be designated and installed in accordance with bs7671.
Fair point !
[automerge]1594195667[/automerge]
The usual reason for TT-ing an out building is the 10mm size of the CPC if it needs bonding to extraneous conductive parts in the out building from a PME-derived supply.

If you are feeding via 10mm or more SWA (with a CPC, or armour of equivalent rating) no issue, but if its a 4mm run then you either need a supplementary CPC or simply isolate it via a TT-ing RCD device and use a local earth rod.

As for the earth mat/rod for an outdoor pool it makes sense. The issue for safety is the voltage difference between the water/metal in the event of a PME fault, and the Earth around the pool. Even if the earth rod/mat is unable to pull the PME fault down close to true 0V, it will still raise the surrounding soil to (hopefully) a small enough difference in potential for anyone stepping out of the pool.

So the reason for isolation the PME earth in the undersized bonding probable with the above example of a 4mm cpc to the remote tub/building supply is that it may not have capacity for an earth fault PFC current ?
Nothing to do with the dreaded lost Neutral/ PEN conductor in a PME supply ?

if this is the case then shouldn’t the best practice to ensure 10mm or equivalent CPC size and in the case of a tub put in a supplementary electrode as low ohm as possible in the supply to the remote application and ensure all extraneous parts are bonded - rather than go with the TT approach the latter seems to be the go to choice for most?

a
 
Last edited:
So the reason for isolation the PME earth in the undersized bonding probable with the above example of a 4mm cpc to the remote tub/building supply is that it may not have capacity for an earth fault PFC current ?
Nothing to do with the dreaded lost Neutral/ PEN conductor in a PME supply ?
It is not the earth fault PFC as that will be cleared by your local MCB no problem, it is the PME fault resulting is a sustained current to true Earth via your externally conductive stuff.

Sure if its only tens of ohms on a small bit of metal then you won't roast a 4mm cable in this example, but the CPC under PME faults potentially carries the residual neutral current of everyone in the faulted section, so it could be tens or hundreds of amps if your Ra is low enough. Having Ra below a couple of ohms is unlikely though, so high tens of amps for long periods is the typical scenario needing 10mm CPC size.

There might well be issues of external metalwork on an out building going high under PME faults as well with a risk for high touch potential like the hot tub case, so TT-ing is an option also.

if this is the case then shouldn’t the best practice to ensure 10mm or equivalent CPC size and in the case of a tub put in a supplementary electrode as low ohm as possible in the supply to the remote application and ensure all extraneous parts are bonded - rather than go with the TT approach the latter seems to be the go to choice for most?
TT-ing is much easier than adding Earth rods/mats for sure, so is the easier option in most case.

If every building had an earth rod on their PME earth then we would have less of a debate/worry as full-on PME disconnection and voltages above 50V to Earth would be much less likely!
 

Reply to 32a supply for a hot tub of a PME supply. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Replies
7
Views
2K
  • Question
No, that is part of a different earthing system, don't mix the different earthing systems unless you have given proper engineering consideration...
2
Replies
27
Views
3K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top