32amp radial | on ElectriciansForums

Discuss 32amp radial in the Commercial Electrical Advice area at ElectriciansForums.net

Joined
Feb 6, 2020
Messages
104
Reaction score
9
Location
london
In a school today helping an approved contractor.

There is a over door fan heater on a 32amp radial fed off a rotary isolator.

It then goes into a bank of 3 switches that are used to control it.

The swtchs are double pole rated at 20 amps.

Isn't that a danger being on a 32 amp 4mm mcb
 
If the heater is over 20A then the switch would be overloaded (even if elements are split) as one is used to switch to whole load.

As it's a fixed load, the cable and switches only need to be rated for the load - not the protective device, so it all depends on the size of the load.
 
Are you sure it's a 20A switch in the drid and not a 32A?
If the heater is over 20A then the switch would be overloaded (even if elements are split) as one is used to switch to whole load.

As it's a fixed load, the cable and switches only need to be rated for the load - not the protective device, so it all depends on the size of the load.


Didnt think you could get a 32amp grid switch...
 

Reply to 32amp radial in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
517
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top