M

melvinmoo

hi just to check my sums are correct I will be running my oven of a 60 amp 3 phase breaker as the oven draws 51 amps I will be using a 5 core 10mm swa lsf cable to a 63 amp commando skt outlet does any one have any issues that may have missed any advice welcome
 
Please don't go there on a warranty issue, heard it all before, that is just pure scaremongering!! Any approved means of connection to a fixed supply (eg, switch fuse / switch isolator /plug & socket etc) that is recognised by BS7671 and you won't VOID any warranty. Double indemnity if the person making the connection to the supply is a qualified electrician!!
 

Reply to 37 kw industrial oven in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top