3a FSU downstream of a spur socket from RFC - compliant? | on ElectriciansForums

Discuss 3a FSU downstream of a spur socket from RFC - compliant? in the UK Electrical Forum area at ElectriciansForums.net

Rockingit

-
Mentor
Arms
Supporter
V.Nearly Esteemed
Joined
May 25, 2011
Messages
6,671
Reaction score
7,047
Location
Somerset
Have a 3a FSU that feeds an adjacent WC light and fan, wired from a socket that is a spur. Even though we all know that it's safe (no different to having a 3a plug top in the socket), can't quite make up my mind if it's compliant or not. Thoughts?
 
spur from a spur. not compliant.

hate to disagree, but whether its a socket, or a 3A fcu... still a spur from a spur.
Perfectly safe, as you say, it could be a double socket with a 3A plugged in... no difference to the load on the cable branching off the ring.... but regs is regs
 
OK - the two polar opposite responses I expected. This application is fixed equipment…
 
My reading of 433.1.204 suggests to me that it’s compliant

“…..Such circuits are deemed to meet the requirements of regulation 433.1.1 if the current carrying capacity (Iz) of the cable is not less than 20A and if, under the INTENDED conditions of use, the load current in any part of the circuit is unlikely to exceed for long periods the current carrying capacity of the cable.”
 
spur from a spur. not compliant.

hate to disagree, but whether its a socket, or a 3A fcu... still a spur from a spur.
Perfectly safe, as you say, it could be a double socket with a 3A plugged in... no difference to the load on the cable branching off the ring.... but regs is regs
There is in fact no reg that says a spur off a spur is not allowed.
We don’t do it because the example diagrams of ways to comply with the only RFC reg don’t show it but it’s perfectly possible to comply with spurs off spurs.
I’ve done it in a large hotel lobby with 5A sockets for table lamps.
 
This is an interesting question.

It goes against the design guide in appendix 15 (no spurs off spurs allowed). However, I don't believe there is any reg stating that app 15 has to be rigidly adhered to in order to comply.

IMO if the total load won't exceed the current carrying capacity of the cable running back to the ring, then it is compliant. In this case 20A for the double socket, and 3A for the FCU = 23A. So compliant if Method C.

Best practice? Perhaps not, the fused spur could easily be repurposed for a higher load. And you can bet a fiver of anyone's money that the next spark would condemn it, as it doesn't meet app 15.
 
Could we also go down the “fixed load” route as a light and a fan aren’t going to overload anyway? Tongue in cheek - no overload protection required unless manufacturer requires it for fan!
 
U
Could we also go down the “fixed load” route as a light and a fan aren’t going to overload anyway? Tongue in cheek - no overload protection required unless manufacturer requires it for fan!
Unfortunately, the fan isn't a fixed load. It can stall and draw increased current.
 

Reply to 3a FSU downstream of a spur socket from RFC - compliant? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
391
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
975
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thanks for the advice.
Replies
11
Views
2K
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top