I'm charging a PHEV from a standard plug socket, and it works. However I purchased an extension and the standard plug going into the socket has melted... it got a bit too warm for a bit too long.

Are there recommendations of specific plugs and cabling that could take 3kw comfortably for constant load?

The extension cable I have is 25m in length as I may not be fortunate to have my car parked directly outside the property.
 
Are you sure your vehicle charges at 3kW? Most chargers that plug in to a standard 13A socket limit the charge current to 10A.
Extension cables rated for the full 13Aare few and far between, and even these will show signs of thermal deterioration if used at full load for long periods.
If the car really does draw 3kW, you may be better looking for 16A plugs, sockets and 2.5mm2 flex.
 
I'm charging a PHEV from a standard plug socket, and it works. However I purchased an extension and the standard plug going into the socket has melted... it got a bit too warm for a bit too long.

Are there recommendations of specific plugs and cabling that could take 3kw comfortably for constant load?

The extension cable I have is 25m in length as I may not be fortunate to have my car parked directly outside the property.
BS 7671 gives a recommendation that any load of 2KW and above should be on a dedicated circuit forv this very reason, tin hat on
 
Are you sure your vehicle charges at 3kW? Most chargers that plug in to a standard 13A socket limit the charge current to 10A.
Extension cables rated for the full 13Aare few and far between, and even these will show signs of thermal deterioration if used at full load for long periods.
If the car really does draw 3kW, you may be better looking for 16A plugs, sockets and 2.5mm2 flex.
Smart meter shows it draws around 2.7kw by itself.

The extension I use is presently this:
  • 13 AMP 240V 3 Pin Black Plug
  • 1.5mm 3183Y Orange Flex Cable
Though I'd note the plug has melted.
 
I recently sat the NICEIC vehicle charging course, and plugging the car into a 13A socket is on its way out as a standard, but they did say that if it was done, the socket would be on its own circuit AND be specially designed and labelled to be suitable for car charging.

Standard sockets can’t cope with a constant 3kW load, never mind the plug.
 
You need to have both a good plug and a good socket. If either is in any way substandard, a meltdown is likely. Historically, 3kW heaters were relatively common and 13A plugs were intended to supply them for hours on end. If you have not tried an original MK 646 plug in an original 2747 socket (or equivalents) you might be surprised as to how well they do handle a constant 13A load. But few are engineered that well these days and we have come to accept that 13A is a push.

This company appears to have addressed the problem of inadequate extension leads for EV charging:

 
Although for the first 20 years of 13A plugs, not many heaters had thermostats. I agree that the constant load of the charger is unusual but it was within the original design intent of BS1363 to handle 13A without damage.

I recall at dad's shop there were sometimes two 3kW non-thermostatic heaters plugged into one double socket running all day long in winter, because the installed heating system did not heat the centre of the showroom sufficiently. The socket ran warm but survived for years.
 
Too some degree it is just a sad reflection of modern "value engineered" products that can't actually handle their rating under any sort of real-world use.

For 13A use then try a single socket (not double) from one of the better suppliers such as MK (but not the crap "essentials" range) or Schneider. For extension lead the problem is not the 1.5mm cable but the quality of the plug, so the same applies.

Also it can help to operate the socket's switch a few times before plugging in, and to plug in/remove a couple of times with the switch off before finally switching on. Reduces contact resistance slightly.
 

Reply to 3kw constant load on a standard plug socket in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
707
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top