Hello all, after some advice please.

I have got a small job installing some 16a commando sockets in a farm workshop. The workshop has a 3ph sub DB on the wall which is fed from the main DB on the other side of the wall, about 25m away. The sub DB is supplied from two lots of 6mm2 twin in 25mm conduit acting as the 3ph supply with a 2 2.5mm2 cpc. The sub BD has a front end 100ma rcd as the whole farm is TT.

Other than all 3 phs being tagged red with no other ID, is this method of install an issue?

The rest of the farm is run in 4core SWA so guessing this one had been done some time ago. Any advice welcome. Haven't done any testing yet so dont know any results.
 
TL;DR
3ph board fed from two lots of twin.
T&E cable has a voltage rating of 300/500 (Uo/U) so theoretically it can be used for 400v supplies. What has been done is somewhat unconventional and you could argue it is a breach of Regulation 521.8.1 but is it a safety issue, probably not.
 

Reply to 3Ph supply to sub panel in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
787
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
612
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top