3ph to domestic property, 80A or 100A? | on ElectriciansForums

Discuss 3ph to domestic property, 80A or 100A? in the Domestic Electrician Forum area at ElectriciansForums.net

Joined
Feb 24, 2019
Messages
28
Reaction score
6
Location
Derby
Customer has asked for DB and new CUs for large dwelling house, WPD are putting in 3 phase to replace 100A single phase and are saying fit 80A main fuses....

Main load on all phases is Tesla wall charger 32A and a ground source heat pump 32A.

Given they are both loads that will run potentially continuous duty cycle, that's 64A, leaving 16A headroom per phase.

There are 2 CUs one with 3 RMs and one for a bunch of lighting circuits. Presuming I wire each CU to a separate phase, that's still not going to be enough unless WPD put in 100A main fuses?

Options, please!

1) Leave the existing 100A single phase in and have 2 meters?
2) Insist they install 100A supply/fuses? That's still only a 36A supply after the two big loads.
3) Split the RM CU and have different floors on different phases? Maybe even add a 3rd CU on L3?

Thx! :)
 
There are 2 CUs one with 3 RMs and one for a bunch of lighting circuits. Presuming I wire each CU to a separate phase, that's still not going to be enough unless WPD put in 100A main fuses?
Is it the 3 RM that you are concerned by? The On Site Guide Appendix A table from domestic final circuts has 100% of the largest circuit + 40% of the remainder, say, 32 + 0.4*(2*32 + 3*6) = 65A
 
65A load for a domestic house? Only if they're growing weed!
True, it seems way too high for any sane activity, but in terms of diversity versus total listed CU circuits it is at least justifiable!
[automerge]1588004200[/automerge]
Actually the lighting should be separate and have a 0.66 factor.
3 RM & 3 lights = 32 + 0.4 * (2*32) + 0.66*(3*6) = 69A and still higher than sane!
But better than 114A
 
is the heat pump existing?
if not, I would suggest a 3phase unit.

can you put in a 3 phase db adj. meter with a feed out to each of the house db's and separate feeds to the big loads (charger and heating etc.)

this will alow you to balance the phase currents as best you can.
 
True, it seems way too high for any sane activity, but in terms of diversity versus total listed CU circuits it is at least justifiable!
[automerge]1588004200[/automerge]
Actually the lighting should be separate and have a 0.66 factor.
3 RM & 3 lights = 32 + 0.4 * (2*32) + 0.66*(3*6) = 69A and still higher than sane!
But better than 114A

How
is the heat pump existing?
if not, I would suggest a 3phase unit.

can you put in a 3 phase db adj. meter with a feed out to each of the house db's and separate feeds to the big loads (charger and heating etc.)

this will alow you to balance the phase currents as best you can.

Acvpridng to the OP it is a three phase car charger and a 3 phase heat pump
 

Reply to 3ph to domestic property, 80A or 100A? in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Don't need to read again the picture tells me what I need. BTW your a bit touchy about solar, it's old hat these days 🤣 and a waste of money
Replies
19
Views
1K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top