I have to wire up an autoclave its 3 ph 415 v 9kw and doing ohms law I get 21.6 amps the question is do I devide this by 3 or would it be 21.6 a per phase
 
9000/(1.732 x 400) = 13A. THIS IS WHAT EACH LINE WILL CARRY.assuming no problem with power factor.
 
Last edited by a moderator:
9000/1.732 x 400 = 13A. THIS IS WHAT EACH LINE WILL CARRY.assuming no problem with power factor.
Although you got the right answer, the equation you passed on is somewhat flawed
Try 9000/1.732 then DIVIDE by 400= 12.99amps (13amps) id like to see the cable size for your 2million+ amps:eek:

Where were you baldsparkie, you missed that one lol
 
Last edited:
Although you got the right answer, the equation you passed on is somewhat flawed
Try 9000/1.732 then DIVIDE by 400= 12.99amps (13amps) id like to see the cable size for your 2million+ amps:eek:

Where were you baldsparkie, you missed that one lol

Now for the CORRECT way! 9000/(1.732x400) = 13A ;)

Sorted!!

Steve.

----------------------------

Learn from your mistakes, but don't make too many or you will know too much
 
Although you got the right answer, the equation you passed on is somewhat flawed
Try 9000/1.732 then DIVIDE by 400= 12.99amps (13amps) id like to see the cable size for your 2million+ amps:eek:

Where were you baldsparkie, you missed that one lol

Indeed I did, must be getting old Darkwood. :D:D:D Glad you have your wits about you mate.

Divide it is multiply its not.:eek:;)

Now for the CORRECT way! 9000/(1.732x400) = 13A ;)

Sorted!!

Steve.

----------------------------

Learn from your mistakes, but don't make too many or you will know too much

Show Off !;):D
 
Last edited by a moderator:
I would only add that you need to check on the auto-clave what its power factor is i.e p.f. 0.8
KVA=KW divided by p.f

so your current rating may well be a little higher (I assume you are looking at circuit protection &/or cable sizing)
 
How about (9000/3)/230. Gives the same result within a few milliamps. And easier way to remember.

If it's a 9kW balanced load, 3kW will be from each phase, therefore divide that by 230V and Bob's your Mothers brother.
 
Last edited:

Reply to 3phase in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Noted. Thank you. Out of phase summation being the answer to the question.
Replies
14
Views
846
To show the varying line voltages you can plot it as a phasor diagram then use Millmans Theorum to calc the voltages wrt supply neutral. There's...
Replies
1
Views
1K
  • Question
The only way to really tell is take an actual amp probe and check it that way. I wouldn’t always depend on your UPS display. You do need a more...
Replies
1
Views
496
  • Question
Anywhere where the normal lights are dimmed or dimmable the emergency lighting should be of the maintained type. So maintained emergency lighting...
Replies
4
Views
981
davesparks
D
  • Question
I’d say yes go for it.
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks