P

peteludman

I have to wire up an autoclave its 3 ph 415 v 9kw and doing ohms law I get 21.6 amps the question is do I devide this by 3 or would it be 21.6 a per phase
 
9000/(1.732 x 400) = 13A. THIS IS WHAT EACH LINE WILL CARRY.assuming no problem with power factor.
 
Last edited by a moderator:
9000/1.732 x 400 = 13A. THIS IS WHAT EACH LINE WILL CARRY.assuming no problem with power factor.
Although you got the right answer, the equation you passed on is somewhat flawed
Try 9000/1.732 then DIVIDE by 400= 12.99amps (13amps) id like to see the cable size for your 2million+ amps:eek:

Where were you baldsparkie, you missed that one lol
 
Last edited by a moderator:
Although you got the right answer, the equation you passed on is somewhat flawed
Try 9000/1.732 then DIVIDE by 400= 12.99amps (13amps) id like to see the cable size for your 2million+ amps:eek:

Where were you baldsparkie, you missed that one lol

Now for the CORRECT way! 9000/(1.732x400) = 13A ;)

Sorted!!

Steve.

----------------------------

Learn from your mistakes, but don't make too many or you will know too much
 
Although you got the right answer, the equation you passed on is somewhat flawed
Try 9000/1.732 then DIVIDE by 400= 12.99amps (13amps) id like to see the cable size for your 2million+ amps:eek:

Where were you baldsparkie, you missed that one lol

Indeed I did, must be getting old Darkwood. :D:D:D Glad you have your wits about you mate.

Divide it is multiply its not.:eek:;)

Now for the CORRECT way! 9000/(1.732x400) = 13A ;)

Sorted!!

Steve.

----------------------------

Learn from your mistakes, but don't make too many or you will know too much

Show Off !;):D
 
Last edited by a moderator:
I would only add that you need to check on the auto-clave what its power factor is i.e p.f. 0.8
KVA=KW divided by p.f

so your current rating may well be a little higher (I assume you are looking at circuit protection &/or cable sizing)
 
Now for the CORRECT way! 9000/(1.732x400) = 13A ;)

Sorted!!

Steve.

----------------------------

Learn from your mistakes, but don't make too many or you will know too much
Different transposition but no less or more the correct way than my solution :p it all gives the same result and thats all you need.:)
 

Reply to 3phase in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
414
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Noted. Thank you. Out of phase summation being the answer to the question.
Replies
14
Views
959
They do a cy type with pur coating and it is even tougher but is shielded
Replies
3
Views
407

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top