I have to wire up an autoclave its 3 ph 415 v 9kw and doing ohms law I get 21.6 amps the question is do I devide this by 3 or would it be 21.6 a per phase
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 3phase in the Electrician Talk | All Countries area at ElectriciansForums.net
9000/1.732 x 400 = 13A. THIS IS WHAT EACH LINE WILL CARRY.assuming no problem with power factor.
Although you got the right answer, the equation you passed on is somewhat flawed9000/1.732 x 400 = 13A. THIS IS WHAT EACH LINE WILL CARRY.assuming no problem with power factor.
Although you got the right answer, the equation you passed on is somewhat flawed
Try 9000/1.732 then DIVIDE by 400= 12.99amps (13amps) id like to see the cable size for your 2million+ amps
Where were you baldsparkie, you missed that one lol
Although you got the right answer, the equation you passed on is somewhat flawed
Try 9000/1.732 then DIVIDE by 400= 12.99amps (13amps) id like to see the cable size for your 2million+ amps
Where were you baldsparkie, you missed that one lol
Now for the CORRECT way! 9000/(1.732x400) = 13A
Sorted!!
Steve.
----------------------------
Learn from your mistakes, but don't make too many or you will know too much
Different transposition but no less or more the correct way than my solution it all gives the same result and thats all you need.Now for the CORRECT way! 9000/(1.732x400) = 13A
Sorted!!
Steve.
----------------------------
Learn from your mistakes, but don't make too many or you will know too much
Well if we're going down that road then the PROPER CORRECT way is
KW________
(VxRoot3xPF)