peteludman

I have to wire up an autoclave its 3 ph 415 v 9kw and doing ohms law I get 21.6 amps the question is do I devide this by 3 or would it be 21.6 a per phase
 
9000/(1.732 x 400) = 13A. THIS IS WHAT EACH LINE WILL CARRY.assuming no problem with power factor.
 
Last edited by a moderator:
9000/1.732 x 400 = 13A. THIS IS WHAT EACH LINE WILL CARRY.assuming no problem with power factor.

This is the one you need. Your measuring an rms value divided by route 3, hence 1.73 also supply voltages are recognised as 400v 3 phase 230 single. Not 415/240 ;)
 
9000/1.732 x 400 = 13A. THIS IS WHAT EACH LINE WILL CARRY.assuming no problem with power factor.
Although you got the right answer, the equation you passed on is somewhat flawed
Try 9000/1.732 then DIVIDE by 400= 12.99amps (13amps) id like to see the cable size for your 2million+ amps:eek:

Where were you baldsparkie, you missed that one lol
 
Last edited by a moderator:
Although you got the right answer, the equation you passed on is somewhat flawed
Try 9000/1.732 then DIVIDE by 400= 12.99amps (13amps) id like to see the cable size for your 2million+ amps:eek:

Where were you baldsparkie, you missed that one lol

Now for the CORRECT way! 9000/(1.732x400) = 13A ;)

Sorted!!

Steve.

----------------------------

Learn from your mistakes, but don't make too many or you will know too much
 
Although you got the right answer, the equation you passed on is somewhat flawed
Try 9000/1.732 then DIVIDE by 400= 12.99amps (13amps) id like to see the cable size for your 2million+ amps:eek:

Where were you baldsparkie, you missed that one lol

Indeed I did, must be getting old Darkwood. :D:D:D Glad you have your wits about you mate.

Divide it is multiply its not.:o;)

Now for the CORRECT way! 9000/(1.732x400) = 13A ;)

Sorted!!

Steve.

----------------------------

Learn from your mistakes, but don't make too many or you will know too much

Show Off !;):D
 
Last edited by a moderator:
I would only add that you need to check on the auto-clave what its power factor is i.e p.f. 0.8
KVA=KW divided by p.f

so your current rating may well be a little higher (I assume you are looking at circuit protection &/or cable sizing)
 
Well if we're going down that road then the PROPER CORRECT way is


KW________
(VxRoot3xPF)


:):(:confused::p;):D:o:rolleyes::cool::eek:
 
Now for the CORRECT way! 9000/(1.732x400) = 13A ;)

Sorted!!

Steve.

----------------------------

Learn from your mistakes, but don't make too many or you will know too much
Different transposition but no less or more the correct way than my solution :p it all gives the same result and thats all you need.:)
 
How about (9000/3)/230. Gives the same result within a few milliamps. And easier way to remember.

If it's a 9kW balanced load, 3kW will be from each phase, therefore divide that by 230V and Bob's your Mothers brother.
 
Last edited:
well i think i know now,:) thanks to all of you for the help and i like the answer pub first:D
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
3phase
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
peteludman,
Last reply from
peteludman,
Replies
18
Views
5,436

Advert

Back
Top