So you have someting against me learning? the only error I seemed to have made so far is not appreciating that I need screened cable between the motor and inverter. Luckily, by seeking help, albeit socially distanced, i discovered before ordering.
Learning is good and should be encouraged,
However, it is difficult for us to understand the entire setup you are planning with the limited information provided.
Perhaps you could post a drawing of how you intend to set this system up.
Just a simple block diagram, we still dot know where in the system this 4 or 5 pin plug is intended to be fitted.
Converting a 3phase machine to single phase is not as simple as putting an inverter inline on the supply cable and changing the motor configuration.
There are serveral other things to consider.
Some have been mentioned but not replied to.
You have mentioned that it must be screened cable from inverter to motor, this may or may not be the case.
It depends on make and model of inverter
Distance of cable run between inverter and motor
Proximity to other cables and equipment
As mentioned before, consideration needs to be made for replacing the original contactors and control gear that is likely to be the wrong voltage and not suitable for being powered by an inverter
Many inverters are Simpley not suitable for running off a domestic socket because of emc filtering, dc leakage, start up surge etc.