Hi there,

Just a quick question. I am rectifying many problems on some 3 phase immersion heater circuits in a plant room. There are 4 pole rotary isolators just before the immersion elements and the earthing arrangement is TN-S.

I noticed that the neutrals are connected into a dedicated linking terminal to the side, as opposed to the 4th pole on the isolator. Is this acceptable? Also, is it UNacceptable to wire the neutrals into the 4th pole of the isolator as a means of isolating the neutral? Would this cause damage to equipment?

I understand that the neutral is deemed to be reliably connected to earth (TN systems), so the neutral doesn't necessarily present a shock risk etc.

I also understand that isolating the neutral before the line conductors can result in overvoltages and appliance/equipment damage etc. The use of late break, early make switches for the neutral can help to overcome this etc.

And of course, if it was a TT earthing arrangement, the neutral should be switched anyway (neutral not reliably connected to earth).

At the moment, I am very much on the side of not isolating the neutral, as it is a TN earthing arrangement and this would prevent equipment from potentially being damaged. Basically, what I am asking is, is this correct?

Kind regards.
BodgeJob
 
Hi there,



I noticed that the neutrals are connected into a dedicated linking terminal to the side, as opposed to the 4th pole on the isolator. Is this acceptable?

Kind regards.
BodgeJob
Absolutely, sounds perfectly normal to me
 
In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe. Isolating the neutral can lead to dangerous overvoltages and equipment damage. So yes, you're right not to isolate the neutral.Additionally, remember that in TN systems, the neutral is grounded, reducing shock risk. In TT systems, the neutral should always be switched. Your approach is absolutely correct; stick with it!
:)
 

Reply to 4 pole rotary isolator... Switch the neutral or not? in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
698
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
790
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

All good thanks, still trying to retire but still finding myself busy as ever. Hope you're well.
Replies
13
Views
1K
For a TN system neutral is deemed at earth potential.
Replies
6
Views
488

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top