I have a query. 4 distribution boards, each fed by 25mm2 double insulated tails (approx 30m away) in a roof void. Only 1 16mm2 earthing conductor for all 4 submains. The earthing conductor is then connected at the first board and looped to the other three boards. Is this acceptable? I thought BS 7671 states that each circuit should have its own CPC.
 
You have probably read a regulation that each individual circuit must have a cpc and interpreted as each individual circuit must have its own cpc.
There is electrically nothing wrong with supplying the distribution boards using the same piece of cable.
true there is nothing electrically wrong with it if the cable is large enough but personally i would rather have a seperate earth with each supply.
 
An installation can only have one earthing conductor, it is defined as being the conductor which connects the MET to the means of earthing.
The term 'main earthing conductor' does not exist in bs7671

Dave please refrain from trying to be smart and always trying to catch people out. I apologise for mister meaner. I'm sure you understood what I meant.
 
true there is nothing electrically wrong with it if the cable is large enough but personally i would rather have a separate earth with each supply.
Not a problem for you to do that if you are installing it, I would think it would increase the quality of the installation in many cases and exceeding the minimum standards is generally a good thing, but it is important to be aware that it is permitted to have a single (suitably rated) cable.
 
Just looking in the regs to find where it says each circuit must have its own CPC and I've come across 543.1.2 in the green book (installation complete in 2011) and it clearly suggests that it is acceptable to have a common protective conductor.
 
Just for reference, its the same in the BYB (page 164)

543A.2 Where a protective conductor is common to two or more circuits, its cross-sectional area shall be:
(i) calculated in accordance with Regulation 543.1.3 for the most onerous of the values of fault current and
operating time encountered in each of the various circuits, or

(ii) selected in accordance with Regulation 543.1.4 so as to correspond to the cross-sectional area of the
largest line conductor of the circuits
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
4 submains with one common CPC
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
40
Unsolved
--

Advert

Thread statistics

Created
atm84,
Last reply from
Spoon,
Replies
40
Views
5,049

Advert

Back
Top