atm84

-
Joined
Aug 7, 2011
Messages
834
Reaction score
94
I have a query. 4 distribution boards, each fed by 25mm2 double insulated tails (approx 30m away) in a roof void. Only 1 16mm2 earthing conductor for all 4 submains. The earthing conductor is then connected at the first board and looped to the other three boards. Is this acceptable? I thought BS 7671 states that each circuit should have its own CPC.
 
You have probably read a regulation that each individual circuit must have a cpc and interpreted as each individual circuit must have its own cpc.
There is electrically nothing wrong with supplying the distribution boards using the same piece of cable.
true there is nothing electrically wrong with it if the cable is large enough but personally i would rather have a seperate earth with each supply.
 
An installation can only have one earthing conductor, it is defined as being the conductor which connects the MET to the means of earthing.
The term 'main earthing conductor' does not exist in bs7671

Dave please refrain from trying to be smart and always trying to catch people out. I apologise for mister meaner. I'm sure you understood what I meant.
 
true there is nothing electrically wrong with it if the cable is large enough but personally i would rather have a separate earth with each supply.
Not a problem for you to do that if you are installing it, I would think it would increase the quality of the installation in many cases and exceeding the minimum standards is generally a good thing, but it is important to be aware that it is permitted to have a single (suitably rated) cable.
 
Just looking in the regs to find where it says each circuit must have its own CPC and I've come across 543.1.2 in the green book (installation complete in 2011) and it clearly suggests that it is acceptable to have a common protective conductor.
 
Just for reference, its the same in the BYB (page 164)

543A.2 Where a protective conductor is common to two or more circuits, its cross-sectional area shall be:
(i) calculated in accordance with Regulation 543.1.3 for the most onerous of the values of fault current and
operating time encountered in each of the various circuits, or

(ii) selected in accordance with Regulation 543.1.4 so as to correspond to the cross-sectional area of the
largest line conductor of the circuits
 

Reply to 4 submains with one common CPC in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
750
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top