4-way extension with trunked flex | on ElectriciansForums

Discuss 4-way extension with trunked flex in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Joined
May 22, 2016
Messages
39
Reaction score
15
Location
IW
I was chatting with a PAT tester who mentioned that he would fail 4-way extensions where the flex had been trunked and the client was using them with appliances drawing 13 amps. His reasoning was that the trunked flex should be de-rated. Would you agree with this?
 
Most four way extension lead ends have instructions for connecting to a 13A plug top. I will always note this on an EICR if they are hard wired to the mains supply.[ElectriciansForums.net] 4-way extension with trunked flex
 
I misread your first post, a four way extension should be wired using 1.25 flex (13A) or 1.5 flex (16A). If it is contained within trunking he maybe theoretically correct depending on the cable csa but personally I think he is pushing the boundaries a bit far.
 
I was chatting with a PAT tester who mentioned that he would fail 4-way extensions where the flex had been trunked and the client was using them with appliances drawing 13 amps. His reasoning was that the trunked flex should be de-rated. Would you agree with this?
This PATester bit simple is he? what idiot is running an extension lead in trunking, wait a sec has someone hard wired this 4 way extension?
 
By trunking I think he meant a plastic u-shaped channel with a snap-on lid. I assume a 13 amp plug would be in use and the "trunking" added to provide some extra protection to the 1.25 flex.
 
I was chatting with a PAT tester who mentioned that he would fail 4-way extensions where the flex had been trunked and the client was using them with appliances drawing 13 amps. His reasoning was that the trunked flex should be de-rated. Would you agree with this?
Might want to derate the OCPD in the plug top, feeding the 4 way extension, if he is that much of a Jobsworth.
 
I have seen this but it isn't that common and I wouldn't worry too much as long as the correct fuse is fitted at the plug top. Extension leads in offices are rarely going to achieve their maximum rating.
 

Reply to 4-way extension with trunked flex in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
159
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
526
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
474

Similar threads

  • Question
After fitting out the first room of downlights.... i expect him to get a bit speedier at fitting them There is so many unknowns to price at this...
2
Replies
25
Views
2K
  • Question
Hello Dave, Thanks for taking the time to reply. I appreciate the info, I haven't updated this post yet, but I have since been talking to some...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top