AJB Temple
DIY
I have a number of circuits in a not very old Hager sub CU, with split RCDs. All of the active circuits (8 used in a 12 slot dual RCD CU) test fine. RCDs tripping fine under test with Megger MFT. However, I have a MTN B140 (40 amp obvs) MCB in the board that has nothing connected to it. ie unused. It's live (230v) at the busbar terminal as expected, but also live at full voltage at the top terminal even if the MCB switch is off.
All of the other MCB's behave as normal, with the switches operating as expected. It's not tripping the RCD, presumably because it is an unused circuit breaker.
Is this just a faulty MCB? Obviously I can swap it out for another one, and I don't want a faulty component in the board.
I'm more curious than anything. Any thoughts on causation?
All of the other MCB's behave as normal, with the switches operating as expected. It's not tripping the RCD, presumably because it is an unused circuit breaker.
Is this just a faulty MCB? Obviously I can swap it out for another one, and I don't want a faulty component in the board.
I'm more curious than anything. Any thoughts on causation?