40A shower disconnection time | Page 2 | on ElectriciansForums

Discuss 40A shower disconnection time in the UK Electrical Forum area at ElectriciansForums.net

oscar21

Nearly Esteemed
Joined
Nov 24, 2019
Messages
553
Reaction score
459
Location
North West
Bathroom with an electric shower wired to the latest regs with a 40A MCB and RCD protection. Is the disconnection time 0.4s or 5s.

Looking at the regs it states fixed equipment up to 32A is 0.4s so everything after that unless it has a socket outlet can be 5s, but its a bathroom where everything needs to be RCD protected so surey it needs to be 0.4s.

We are talking about writing a figure on a bit of paper here by the way to satisfy a council bod, not to prevent any sort of injury or death, just a written number. Honestly, I cant wait to retire, it cant come quick enough.

I was previously under the impression that every final circuit now needed to be 0,4s so was surprised to see that stuff over 32A could still be 5s.
 
Maybe 1/10 slower but at a vastly different fault current!
The RCD trips at 30mA in 0.3s, that fast enough to save most people from a fatal shock.
The 40A MCB trips at a current in the hundreds of amps in 0.4s

The 0.4s is to keep touch voltages down, prevent damage to cables from long durations of high current faults and that sort of thing.
That cant be right, the RCD "starts" to trip at 30mA but it depend what bit of the sinewave its at, in 300ms it could be peak voltage and current.

If you've ever had a shock from an RCD protected circuit you'll know it hurts just as much as non RCD, it just doesnt last as long.
 

Reply to 40A shower disconnection time in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
830

Similar threads

  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top