Afternoon. Apologies if this has already been discussed at length - I haven't lurked for a good few months due to some personal issues. Just wanted to throw this one out there and see what the consensus is. I may just be having a daft moment and missing the obvious.

Existing sodium bulkheads installed on external wall fed via contactor. Each luminaire is fed from a Klik Rose, mounted above the suspendsed ceiling. Most of the fittings have failed.

Proposal is to replace with the equivelant 'black box style' LED bulkheads. However, obviously the existing arrangement is a plug and socket under 32a, which made me think about 411.3. 3 and the requirement for all sockets below 32a to hve RCD protection.

Should this now be applied as the fitting is being replaced? Or is an essential "straight swap" of the luminaire (essentially an appliance) simply maintenance and no changes to supply required.

Appreciate the RCD is desireable but just wondering what the consensus is. I'm assuming a straight swap of the appliance on the end of the flex from the Klik classes this as maintenance and no work further back required.

Cheers
 
agree with the last bit. it's a like for like maintenance issue, so the circuit does not need to be uprated to current edition. also.....

see note 3 on that reg. (lighting circuit)
 
Is a klik rose actually classed as a plug and socket ?
agree with the last bit. it's a like for like maintenance issue, so the circuit does not need to be uprated to current edition. also.....

see note 3 on that reg. (lighting circuit)

D'oh. Yes, just looking at note 3. Thnks!
 

Reply to 411.3. 3 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
444
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Ye smaller board (containing the RCBO'S) will literally be next to the MEMSHIELD, And hence the 32A MCB be simply feeding power to a 32A RCBO I...
Replies
5
Views
2K
Promised a photo…. Remember, this was working…. And they managed to move in without hitting it…
    • Like
Replies
4
Views
368

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top