Hi all,
Got a bit of a problem with a new generator when starting a 60hp motor.
It's a 250kva generator with a 125A mounted plug, the plug is protected by a C125 A Merlin gerin c120h MCB with combined 300mA RCD, the motor starts fine but when it changes over to delta it trips the 125A mcb (I temporarily removed the rcd to prove it wasn't that as the are coupled together)
The motor is a 45KW 60hp motor, it is driving a hydraulic pump (tripping with no real load on the motor). After a few goes it will eventually hold, I'm guessing the oil heats up a bit and isn't as thick.
I have done an insulation test between the windings and to earth and all is good, all phases are balanced aswell, the motor is only 2 years old, full load current is 82A if I remember correctly, timer set at 5sec with an 80ms delay between star and delta
So I am putting this purely down to inrush current, will putting a D125 on it resolve this problem of tripping, I have tested using a clamp meter and under some circumstances the current peaks at 150amps for a split second.
None of this was an issue with he old generator however the plug was protected by a 150A MCCB no rcd.
Got a bit of a problem with a new generator when starting a 60hp motor.
It's a 250kva generator with a 125A mounted plug, the plug is protected by a C125 A Merlin gerin c120h MCB with combined 300mA RCD, the motor starts fine but when it changes over to delta it trips the 125A mcb (I temporarily removed the rcd to prove it wasn't that as the are coupled together)
The motor is a 45KW 60hp motor, it is driving a hydraulic pump (tripping with no real load on the motor). After a few goes it will eventually hold, I'm guessing the oil heats up a bit and isn't as thick.
I have done an insulation test between the windings and to earth and all is good, all phases are balanced aswell, the motor is only 2 years old, full load current is 82A if I remember correctly, timer set at 5sec with an 80ms delay between star and delta
So I am putting this purely down to inrush current, will putting a D125 on it resolve this problem of tripping, I have tested using a clamp meter and under some circumstances the current peaks at 150amps for a split second.
None of this was an issue with he old generator however the plug was protected by a 150A MCCB no rcd.
Last edited: