D
davesparks
I agree the MCb is the problem, but harder to intigrate RCD protection with an mCCB
I have been down turned up the star delta change over time, helped a bit, but he said it also tripped once mid ride, far from ideal. So reluctant to keep the C125, measured it with my clamp meter with max function and it peaked at 175A, also measured earth leakage, it was around 30mA until the motor was started, meter maxed out then dropped to 120mA while motor was running, but I'm unsure if he meter would accurately read when the motor starts as there's such a high inrush. The next question is the RCD time delayed, I don't know it doesn't say type S. See picture this is what they have at the moment, as you can see not easy to fit anything other than this set up. This box supplies a 63A, 2x 16A and 32A. There is an main RCD on the generator but have this turned off as a fault in one ride cannot shut the whole lot down when they are open.
I'm not sure what to suggest.
It's not too hard to integrate earth leakage protection into an MCCB, just fit a shunt trip operated by an earth leakage relay.
How does the generator behave when the mcb trips? Does it throw up any faults, lose speed, send up a cloud of black smoke etc?
Switching out the main RCD on the generator may not be a very sensible idea, and may not be compliant with the requirements of bs7909. You should adjust the tripping current and time delay in order to achieve discrimination.