Morning all,

I‘d really appreciate some advice - not a kick in the pants please - from those more knowledgeable than me!

My new kitchen and utility room are each supplied by 4mm T&E radials. Each circuit is protected by a 32A RCBO.

Kitchen
  • Single oven rated at 2.5kW connected to single socket at end of radial
  • Toaster, kettle, fridge and microwave connected to 3 x double sockets leaving some spare

Utility
  • Washing machine connected to single socket
  • Vented dryer connected to single socket
  • Boiler connected to 3A fused switch
  • 2 x double sockets spare

Length of radial in both cases is less than 10m so no worries there.

I was told that a 4mm radial with 32A protection is a ’standard circuit’ but there are issues with the installation that bother me, specifically:

1) The oven is not on a separate circuit so it’s not a ‘standard circuit‘ at least according to the OSG
2) The cabling for the most part is clipped direct but it is boxed in with other loose cables for a run of about 2m.
3) All the cables from the consumer unit descend loosely through a void in an otherwise insulated stud wall before going their separate ways (I suspect my OCD is kicking in with this one)

My worry of course is the possibility of the 4mm cables becoming overloaded at less than 32A.

Please understand that rewiring either of these circuits or installing new ones would involve huge disturbance which I am very keen to avoid.

I would sleep easier if the RCBOs were down rated to 25A but Wylex only make compact types for this rating which wouldn’t match the others in the CU.

I’d really appreciate your advice on this. Best response would be to tell me it’s fine, that I’m overthinking it and should get a life!

Thanks, J
 
I wonder if the OP can post some photos of the cable run to take a look? Also a detailed photo of the Wylex board to see what it is using?

Certainly changing to a 25A RCBO would deal with most installation methods for 4mm, the question is if one can be sourced for the board. I'm willing to bet that @westward10 will know chapter & verse of what can be fitted!
 
4 mm radials are the future and are absolutely fine.

we are the only country in the world who do rings. What does that tell you.

in my opinion rings are potentially dangerous and I don’t do them any more. Radials every time for me.

personally I would have liked to put the oven on a separate circuit, but each electrician to there own.

ask 5 electricians what they think of an installation design you will get five different answers.
 
4 mm radials are the future and are absolutely fine.

we are the only country in the world who do rings. What does that tell you.

in my opinion rings are potentially dangerous and I don’t do them any more. Radials every time for me.

personally I would have liked to put the oven on a separate circuit, but each electrician to there own.

ask 5 electricians what they think of an installation design you will get five different answers.
I agree with you statement about each to their own, talking about other countries, the radials are multiple just like we had before RFC, talking in general for instance 20A radial unlimited socket outlets is IMO ridiculous. I would never create such a circuit.
I remember at college in one of the craft principles book on craft theory (J F Whitefield) socket radials were limited cant remember the amounts between 15A and 30A circuits.
 
A big thanks to everyone who replied - what a wonderful resource this is!

Let me just clarify that at no point are the cables covered in insulation. They are mostly clipped direct and exposed but for about 2m they have been boxed in with sheet timber and plasterboard. They cables are all loose within what might be thought of as trunking.

Having said that, and before it kicks off in here, I‘m sure every contributor is correct in what they say, namely:

  • Is the installation safe as it is? - Yes
  • Is it well-designed and compliant with the letter of the regulations? - Probably not

I have spoken to the Electrician who did the work and who issued the paperwork. He clearly had the hump being challenged and was adamant that the installation was a standard One. He said that Wylex RCBOs rated at 25A are available despite not being listed in the catalogue.

He’s willing to swap the two over if I insist but can’t do it until early April. For peace of mind, I’ll likely go this way and swallow the £200 he quoted. I’ll keep the 32A ones as back up in case the new 25A ones drive me nuts tripping all the time.

Thanks again to all.
 
we are the only country in the world who do rings. What does that tell you.
You haven't done much research. The ring final circuit is used in other countries as there are other countries that do use BS7671 as their electrical regulation standard
 
I agree with you statement about each to their own, talking about other countries, the radials are multiple just like we had before RFC, talking in general for instance 20A radial unlimited socket outlets is IMO ridiculous. I would never create such a circuit.
I am afraid I can't remember back before we had RFC's or Ring Circuits.

Bit short sighted to think that radials will have unlimited socket outlets, they are restricted in number in all other countries that use them, legislation will change with the advent of any new regulations.
 

Reply to 4mm radials in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Why aren't you asking them?
Replies
5
Views
862
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top