4mm spurred from ring main | Page 2 | on ElectriciansForums
Discuss 4mm spurred from ring main in the UK Electrical Forum area at ElectriciansForums.net
London
32A ring main, adding 2 more sockets off this, spark I’m working with says add radial 4mm to 2 new sockets from ring I’m saying extend ring? I know 4mm can take 32A but I wouldn’t do it his way
Yes this ones been done to death, result is it's not a proper ring according to the informative appendix, but it can't cause an overload on the short leg as long as the joining point is more than iirc 15% of the way round the ring therefore it's ok in terms of minimise the chance of overload. Even with 2 double sockets near the end of a ring eg kitchen you could get overload so it's always a balance, just the 4mm spur stops the physical layout working in your favour.
Reply to 4mm spurred from ring main in the UK Electrical Forum area at ElectriciansForums.net
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Haha yes, it is. Must be a northern expression. Have a Google 😂