E

egginyourface

evening all,

I was told to run 2.5 cable from fuseboard to supply a 3.5 kw single oven. Job is done....

Now they've said theyre going to put in a 5.3kw double oven in.

Question i have is can I apply diversity to this and keep 2.5t+e or do i need to run a new 6mm,

advice would really appreciated

thanks
 
Post 41 &42 dont start back pedaling now.
post 41 and 42?.....I see that your fairly new to the forum Taffy.....well its good to have you on board.....but please feel free to take a look at previous threads i have posted on...stick around for a while ....i think you will find i dont backpeddle on anything...lol......
 
Agreed, however, the old 17th regs book and OSG are different from each other:D

One says 30% of remainder and the other says 30%.

Not sure which way round though.

As i understand it one says something like 10 amps and 30% of remainder and one says 10 amps and 30% of full load above 10 amps, which I think is the same thing. May be wrong here but I think its one of the many examples of confusing tech speak in BS.
 
post 41 and 42?.....I see that your fairly new to the forum Taffy.....well its good to have you on board.....but please feel free to take a look at previous threads i have posted on...stick around for a while ....i think you will find i dont backpeddle on anything...lol......

Yes mate I am ;-) ever thought of taking up a career in law?
 
Glennspark makes great points time and time again, and in this case he's not wrong. However I think there are two sides with this story.
Yes you can calculate and use diversity to install the appropriately rated cable, this is the correct way to do it taking all factors into consideration.

But.. (and this is the way I like to do it) with an oven we know that in the future there could likely be installed a bigger/more powerful oven, or a bigger family in the house so for ease of future install install a bigger cable that would hopefully take that larger future load. This is what I do so once that cables in there's no thought of it being upgraded for sake of being an underrated cable.

:21:
 
yes but even then you can go up a CCC in cable...after diversity has been taken into account.....so, say what could be ample (2.5) for instance this CSA after calculation..not guesswork....so say a 2.5 could then become a 4.0mm for the purposes of future proofing.....so if you start with 6.0mm CSA...then decided to futureproof that...whats it then?....10mm CSA...?....thats 64A for method C...(clipped direct).........totally ridiculous ...not to mention unneccesary.....anyway.....you follow the manufacturers instructions first....they take presidence........
 
Last edited by a moderator:
yes but even then you can go up a CCC in cable...after diversity has been taken into account.....so, say what could be ample (2.5) for instance this CSA after calculation..not guesswork....so say a 2.5 could then become a 4.0mm for the purposes of future proofing.....so if you start with 6.0mm CSA...then decided to futureproof that...whats it then?....10mm CSA...?....thats 64A for method C...(clipped direct).........totally ridiculous ...not to mention unneccesary.....anyway.....you follow the manufacturers instructions first....they take presidence........

You really should go on a 5 week course and then you would fully understand that Diversity are a dance group from Britain`s Got Talent. ;-)
 
only talent i see is when were going past the uni`s here in leeds......loads of fit student birds hanging around the "halls of residence"......yummy.....:drool5:
 
Diversity on a cooker works fine until Xmas day when they trip out. personally I think regs are out of date on this one. Take a 10 kW electric range cooker. 10kW/230V= 43 amps. 10 amps plus 30% remaining load (approx 9.9amps) =19.9 amps so 2.5mm twin and earth on a 20 amp, dont think so. "At the installers discretion" is a term we ought to use more. On top of that you`ve got an appliance that draws for long periods of time allowing heat to build up in the circuit. Its not like a kettle that runs for a couple of minutes at a time. 6 or 4mm on this OP specs every time for me,

Never once heard of an electric cooker tripping out because of diversity being applied.
The cooker diversity formula works for cookers upto 15KW. It's been around now for 60 years, Because it WORKS and it is, no-way out of date. As i've so often stated on these cooker theads, the manufacturers always state the connected load, not the ''maximum load'' which, is always going to be smaller...

The oven elements will not be on constantly, they are all thermostatically controlled, so it's an on and off situation for the duration once upto tempreture...
 

Reply to the thread, titled "5.3 kw double oven on a 20 amp fuse with 2.5 cable" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top