The circuit in itself although not ideal is compliant. If you have concerns why not have a chat with the installer.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 5 kitchen sockets from 1 FSU in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
AKA 'breakfast'. With this setup you can't cook breakfast. Inconvenient.Don't ask for bacon cooked on the George Forman, a cup of tea, toast and microwaved scrambled eggs at the same time whatever you do
This addition was done this week. The other electrics were completed in Feb
now you are trolling, ridiculousAlso, I'm a little uncomfortable, given the number of radio ads about overloading four way bars are fires. Not least since the install is the reinstatement after a fire
Post #6 Trev, an afterthought after 3 months.The guy came up with this arrangement on a rewire? Crikey!
Well spotted DaveyPost #6 Trev, an afterthought after 3 months.
433.1.1 said:Every circuit shall be designed so that a small overload of long duration is unlikely to occur
433.1.1(i) said:The rated current or current setting of the protective device (I[SUB]n[/SUB]) is not less than the design current (I[SUB]b[/SUB]) of the circuit