GN3 clearly says load to be disconnected.
40ms rcds are rated at 40ms to limit touch voltages from rising above 50 in the event of a fault- as I understand it.
200ms and 300ms rcds won't do this.
 
GN3 clearly says load to be disconnected.
40ms rcds are rated at 40ms to limit touch voltages from rising above 50 in the event of a fault- as I understand it.
200ms and 300ms rcds won't do this.

Hi Mike,
Its the Zs value of a circuit that limits the touch voltage to below 50, not the disconnection time.
This is the reason why the maximum Zs permitted by BS7671 for a circuit protected by a 30mA RCD is 1667 Ohms, because 1667 Ohms x 30mA= 50.01v.

I think it creates confusion when the regs refer to the different purposes of RCD's because additional protection refers to backup against the failure of basic protection ie insulation being broken and allowing contact with live conductors.

Zs values provide fault protection but offer no basic protection.

Clear as mud eh? :D
 
So if a RCD trips at 67.3 at x 1 then that would be a fail?


No it's >200mS for the oldertype BS and >300mS for new BSEN types as SES said.

I must ask are you qualified if so GOD HELP US

At 40.4 it has failed as according to the regulations written by my colleagues at the IEE,
 
Last edited:
No it's >200mS for the oldertype BS and >300mS for new BSEN types as SES said.

I must ask are you qualified if so GOD HELP US

At 40.4 it has failed as according to the regulations written by my colleagues at the IEE,

Interesting that you`d consider that as a fail, Ian
For me, the device has not failed, because when the loads are removed it passes the prescribed test.
However, if you`re saying the cct has failed to comply, i`m inclined to agree with you and other ways of complying must be sought.
Would you agree or otherwise that this distinction should be made?
Or have i misinterpreted your statement?
 
Last edited by a moderator:
I was under the impression that you tested RCBO's direct at the RCBO its self with no load and its earth lead dissconnected am i wrong?:confused:
 
An RCd has a particular charecteristic,it is this charecteristic that is under test, not this charecteristic and any other items that may be loading the circuit and giving false readings

Failing an installation for 40.4 x 5 would be very harsh and may not reflect the manufactureres declaration of the units conformity,
The RCd tests are after all only functional tests of the operation of the rcd
Who is to say that the test instrument/tester may be the failure .not the unit,
 

Reply to 5 x Trip 40.4 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
501
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
974
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
877
davesparks
D
Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
618

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top