thanks that helps alot but how does it stand with sockets and lighting on rcds?
as far as i know it is not needed unless in an office enviroment, and no computers???
there are no previous pir's so do i need to draw up any plans? i know straight away a remedial will be no identification on sockets and switches.
Great advice from IQ you do need to know the BRB and GN 3 for testing either on initial verification or PIR. Technically PIR's are quite straight forward for as in as much with you being the competant person
You decide what tests are to carried out on the installation. Remember it is not expected for you to have to dismantle the entire installation to carry out a PIR, you decide what needs to be sampled.
What is difficult about PIR's is what I call the leg work. Getting access to places and circuits is the main. As you highlighted no drawings is another main concern. You have no obligation to provide drawings but you do have an obligation to provide charts for the circuits, as you will need to identify and then label each circuit, but this will be reflected in your price. I have seen me spend over 10 days doing a PIR in a factory/office complex and the majority of that was tracing circuits. PIR's in commercial installations can be the hardest work to be taken on and if your not competant in doing this then you will struggle. Could you not get another more experienced sparks to come in with you and help, 2 heads are definately better than one, and split the quote.
What makes me feel you will struggle is your not certain about lights and RCD. The regs are quite clear on this;
Lights 522.6.5 and 522.6.6
Sockets 411.3.3 522.6.5 and 522.6.6
Computers are slightly different as if they are supplied by BS 1363 sockets and plugs you have to adhere to above. If they do not come under those regs then you can work to Regs 314.1(iv) and 531.2.4
Also if you Selv (reg 411.8) or Pelv (reg 411.7) then there is no need for RCD protection for sockets.
As in anything in life you will need to do this with confidence, I can't stress enough how horrible it is to be stood in front of a TP+N board with cable going everywhere and you have got to sort it out. You have to know the basics just to start.