C

Chris Dolby

i have been doing cable size calculations and just cant get this to work out. i mite be missing something.

here are the numbers ive got to work with. theres 10 72w fluorescent fittings so need to be x by 1.8??) on a 6A cb. the two way switches need to be 50m away from original switches. the problem i keep getting is volt drop not being inside the 3%. surely this must be possible to do in 1 or 1.5mm three core. or will i have to split the lights up onto more switches???
 
have the light switches control a relay rather than the load of the lighting.

spot on, thanks. havent ever bin asked to do such a long run for a 2way,
something i am also unsure about is when calculating cable size for a 2way for the strappers would you double the distance of the three core length, because the live travels down one wire and back on another. just wondered if anyone had any input???
 

Reply to 50 meter cable run for 2way lighting in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
349
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
895
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
If it is TT then you can use the armour of any of them as CPC but will almost certainly need an up-front delay RCD at the sub-main feed point to...
Replies
5
Views
952
  • Question
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...
2
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top