M

midgetman

esternal 500w security lamp 30 meter run
what type and size of cable?
clipped externally
 
esternal 500w security lamp 30 meter run
what type and size of cable?
clipped externally

Cable Calcs, come on mate... You can do them, we all have to ;)

:thumbsup

The 500 watt lamp is going to draw 2.17 amps so you'll be looking to use 1.5mm providing (and you can get your book out and check this) that your voltage drop allows it;) I know the answer but you've posted a lot of questions this evening and it's only fair to get your brain in gear too rather than rely on everyone else to feed you the answers, how do you know what you're being told is correct???:)

I personally wouldn't like to be running a cable for 30m just clipped externally. Can you give us more information regarding the route?

:thumbsup
 
well this says 1.0mm i was just checking it like ------------------------

Supply voltage = 230 Volts
Ib - design current = 2.2 Amps
Protective device type = MCB type B
In - protective device rating = 6 Amps
Length of run of cable = 30 metres
Power factor = 1

Cable Type : Flex

Installation Method : Single-core or Multi-core cables Fixed on (clipped direct), or spaced < 0.3 x cable diameter from a wooden or masonary wall
method C

Ambient temp = 35 °C
Number of circuits including this one = 1
Length of cable in thermal insulation = none

Apply Correction factors:
From TABLE 4C1 : Cg = 1 (Grouping)
From Table 4H3A : Ca = 0.91 (Ambient temp)
From TABLE 52.2 : Ci = 1 (Insulation)
Protective device factor : Cc = 1

It = tabulated current carrying capacity
It = In / (Cg x Ci x Ca x Cc)
It = 6 / (1 x 1 x 0.91 x 1 )
It = 6.59 Amps
From TABLE 4F3A Cable selected = 1 mm²

TABLE 4F3B For 1 mm²; mV/A/m = 46
mV/A/m corrected for power factor = mV/A/m x Power Factor = 46 x 1 = 46

Voltdrop = (mV/A/m x Length x Design current) / 1000
Voltdrop = ( 46 x 30 x 2.2 ) / 1000
Voltdrop = 3.04 Volts
(Maximum permissible voltdrop (regulatuon - 525) = 11.5 Volts)

Calculated Cable size = 1 mm², Minimum Earth conductor size = 1 mm² (Table 54.7)

Maximum Cable Length = 113.6 Metres
 
I assume you are using SWA
For one lamp at that distance there is no problem. However,..... be assured for yourself and do the calculations, plus you may want to future proof the circuit.

and you are going to clip the cable direct ... to what? You might consider laying along side a path or under pathway slabs?
 
well spotted

Cable-Mate Version 4.6.0

Cable ID / REF number :

Supply voltage = 230 Volts
Ib - design current = 2.2 Amps
Protective device type = MCB type B
In - protective device rating = 6 Amps
Length of run of cable = 30 metres
Power factor = 1

Cable Type : Flex

Installation Method : Single-core or Multi-core cables Fixed on (clipped direct), or spaced < 0.3 x cable diameter from a wooden or masonary wall
method C

Ambient temp = 35 °C
Number of circuits including this one = 1
Length of cable in thermal insulation = none

Apply Correction factors:
From TABLE 4C1 : Cg = 1 (Grouping)
From Table 4H3A : Ca = 0.91 (Ambient temp)
From TABLE 52.2 : Ci = 1 (Insulation)
Protective device factor : Cc = 1

It = tabulated current carrying capacity
It = In / (Cg x Ci x Ca x Cc)
It = 6 / (1 x 1 x 0.91 x 1 )
It = 6.59 Amps
From TABLE 4F3A Cable selected = 1 mm²

TABLE 4F3B For 1 mm²; mV/A/m = 46
mV/A/m corrected for power factor = mV/A/m x Power Factor = 46 x 1 = 46

Voltdrop = (mV/A/m x Length x Design current) / 1000
Voltdrop = ( 46 x 30 x 2.2 ) / 1000
Voltdrop = 3.04 Volts
(Maximum permissible voltdrop (regulatuon - 525) = 6.9 Volts)

Calculated Cable size = 1 mm², Minimum Earth conductor size = 1 mm² (Table 54.7)

Maximum Cable Length = 68.2 Metres
 

Reply to 500w security lamp 30 meter run in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

Thanks for that, issue now sorted.
Replies
2
Views
724
I'm not sure on the environmental implications, a good quality integrated fitting will last many years and be more energy efficient than the GU10...
    • Like
Replies
13
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top