Well, after being back on site I have found there is continuity between the load supply and the output wire to the element without the relay connected. There is also slight continuity between L-E (and hence TN-C-S slight continuity barely readable with earth). I could not fully isolate the unit today to test as it is installed in a 24hr McDonalds that has a load of other appliances running off the circuit which they could not afford to go down and at the moment the elements are giving out 52 degrees which is not quite the 66 set point, but they would rather have that than me turn it off for 30mins!!
However all that said if the relay is bypassed and supply to load is connected directly then the elements heat correctly which I was expecting anyhow. The controller is definitely fine - it gives out a steady 24VDC supply and energises and de-energises the load upon the correct input signals.
This leads me to believe there is an insulation problem somewhere along spaghetti junction - but still does not explain why this one relay gives out 120V with the fault and a brand new replacement gives out 0V. The relay which I did remove and tested works perfectly well on the bench.
I suppose there could still be a faulty element - just because it heats doesn't mean it isn't leaking somewhere.
My heads melted with this now!
I have found there is continuity between the load supply and the output wire to the element without the relay connected.
However all that said if the relay is bypassed and supply to load is connected directly then the elements heat correctly which I was expecting anyhow. The controller is definitely fine - it gives out a steady 24VDC supply and energises and de-energises the load upon the correct input signals ... but still does not explain why this one relay gives out 120V with the fault and a brand new replacement gives out 0V. The relay which I did remove and tested works perfectly well on the bench.
Sorry to jump in, but does anyone have any simulation software for PID control. It's a subject that we haven't covered on my HNC (even though weirdly I'm one assignment away from a distinction in this module).
It's something I'd like to understand fully, not just the textbook version of how they're supposed to work.
Sorry to jump in, but does anyone have any simulation software for PID control. It's a subject that we haven't covered on my HNC (even though weirdly I'm one assignment away from a distinction in this module).
It's something I'd like to understand fully, not just the textbook version of how they're supposed to work.
Reply to 50A SSR Problem in the Commercial Electrical Advice area at ElectriciansForums.net