Hi, I have been approached to install a 50kwp Pv system for a very local industrial client.
I have been a little worried about + 4Kwp installs but as the client is only 100yds from my door I thought id get my feet wet.
First off i would appreciate any general advice when quoting, installing and commissioning a 50kwp installation.
Secondly I have an issue with a 35mm sub-mains cable my competitors all want to use to connect the system. The cable is 35mm 4 core swa with a total length of 160m approx. So far the two other companies have said this cable is fine but I cannot see how. By any calc I do it fails miserably on volt drop even at 3%. Ive read PV should be 1%! Am I doing something wrong or have my competitors not bothered to calculate this?
Hats of to mark c, you seem to know your stuff!
Thanks,
Austin Gregg
I have been a little worried about + 4Kwp installs but as the client is only 100yds from my door I thought id get my feet wet.
First off i would appreciate any general advice when quoting, installing and commissioning a 50kwp installation.
Secondly I have an issue with a 35mm sub-mains cable my competitors all want to use to connect the system. The cable is 35mm 4 core swa with a total length of 160m approx. So far the two other companies have said this cable is fine but I cannot see how. By any calc I do it fails miserably on volt drop even at 3%. Ive read PV should be 1%! Am I doing something wrong or have my competitors not bothered to calculate this?
Hats of to mark c, you seem to know your stuff!
Thanks,
Austin Gregg