Hi all,
After some advice.

i have a run of 50mm 4 core on a farm to reinstate some GP buildings.
100A feed, with fused disconnect at the origin.

in its run it needs to be intersected to feed a small existing 3phase board just for some lightingin a tractor shed.

my thoughts are use a non fused isolator. The only issue im finding is sourcing one I can get x2 50mm cores into the incoming side none I can find (for a decent price) use lug mounted posts.
Other option in my mind is a busbar chamber?
Any help much appreciated!
 
I know it's a terribly old fashioned idea these days but why not just breech joint it underground and bring a 25mm SWA in to the tractor shed.
That way the 50mm remains an uncut continuous cable through to its final destination and you don't have to try and get a 50mm in to a small DB.
 
I know it's a terribly old fashioned idea these days but why not just breech joint it underground and bring a 25mm SWA in to the tractor shed.
That way the 50mm remains an uncut continuous cable through to its final destination and you don't have to try and get a 50mm in to a small DB.

the route the 50mm takes goes through the tractor shed in any case
 
the route the 50mm takes goes through the tractor shed in any case

In what way? Does it come up from underground, travel through the shed then go back underground or is it going under the shed?

If its going to be surface mounted in the shed anyway then I'd either still use a breech joint if possible or install a steel box with bolted terminal blocks in it and take a smaller SWA off to the local DB.
 

Reply to 50mm swa disitribution advice in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
787
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
707
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top