As we know, Type A RCD's are favourite for many circuits (in terms of Socket outlets, lights etc)

At our site most of our lighting is now LED - we've been swapping them out as a combination of upgrade and just remedial works. However, as they're all on Klik roses we haven't had anything to do with the boards - so the circuits are still sat on their AC RCD's.

At what point does one have to 'decide' that the DC currents will blind an AC and I need to change the existing RCD's to A?

In my eyes the job is "maintenance" - but at the same time we haven't really "replaced like for like" - as we don't fit fluorescents anymore.

This made me wonder how domestic folks approach this. For example, - if you change Mrs Smiths 8ft fluorescent in her kitchen because it has failed or she wants something brighter, is that enough to tell her it can't be done unless a Type A is retrofitted to replace her old AC one?

It's frustrating that there's no figures given for acceptable DC leakage. Leaves it a bit vague surely?
 
You have made a really interesting point.

If you have changed something for maintenance then a like for like replacement needs no further thoughts or considerations.

however, if it is not a true like for like replacement then due consideration should be given to how it affects the circuit protective devices.

a similar but slightly more obvious one would be replacing light switches with fancy metal faced ones when there is no cpc available at the switch point.

there is no simple answer other than we should consider how the changes we make to any circuit affect its safety and not just blindly follow a reg. that we think should cover our behind.
lets face it, if the changes we make reduce the safety and someone gets hurt, we could end up spending some time in court and nobody wants to be in that position.
 

Reply to 531.3.3 & Maintenance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
769
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

  • Question
those old mk rcds are very fast the figure you have quoted is the maximum allowed not the typical times,I have seen mk ones trip at 9 ms , the...
Replies
5
Views
2K
OK for a simple load. What happens with (say) SMPS LED drivers ? I'd guess : Loads aren't perfectly balanced, especially during startup, so one...
Replies
8
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top