Hi all,
Doing a new build barn conversion installation and the lighting has been designed by a consultant. They've specified some 5A sockets for plug in lamps.. never done these before although I know the plugs and sockets are available.. round pin type.
Some of the arrangements are for 2 way switching so am I right in thinking the only way to do this is to treat the socket as basically the lamp and switch it locally using standard 2 way switches and intermediates adjacent to the sockets?
I'm planning to use dedicated 6A radial circuits using 1.5mm t&e does this sound ok?. There are a maximum of 6 outlets on each radial ..
Cheers..
 
You can put the switches where you want but three plating won't be practical as the sockets don't have loop in terminals so bring the live and neutral to the switches and connect that way.
 
Ok...., I do have plenty of ways in a 16 way con unit though so I thought it would give a bit of convenience to put all the 5A lighting skts on a separate mcb. I think there's 3 x 5A radials, 2 upstairs and 1 downstairs so these could go in one or maybe 2 mcbs.
 
about 5 years. Yes I agree it would be easiest and cheapest option to have them all on lighting circuit. just thought as I have the spare ways at dB it would bnice to segregate them. it's quite a large and complex lighting circuit as it is with sensor ensuite lights and extra wall lights everywhere etc. thanks for all helpful replies..
 
about 5 years. Yes I agree it would be easiest and cheapest option to have them all on lighting circuit. just thought as I have the spare ways at dB it would bnice to segregate them. it's quite a large and complex lighting circuit as it is with sensor ensuite lights and extra wall lights everywhere etc. thanks for all helpful replies..

Wouldn't it be better to split the one large lighting circuit into two smaller ones?
 

Reply to 5A lighting sockets circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Replies
2
Views
314
Hello Brianmoooore, Thanks for yor reply - Sorry that I did not see your message until today - the Forum replies notification emails about your...
Replies
7
Views
672

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top