6 Amp RCBO 13 Amp load | on ElectriciansForums
Discuss 6 Amp RCBO 13 Amp load in the UK Electrical Forum area at ElectriciansForums.net
Top Cat
Gloucester
Doing a rewire at the moment in an empty house. I am using RCBO's mostly so when i got 1 room complete i wired the 4mm radial into the RCBO so we could get the kettle going.
After several brews i went to disconnect it only to find i had wired it into a 6 Amp RCBO!
The trip never operated once with a 3 KW kettle on it. It was a Square D RCBO.
Going to swap the breaker on Tuesday when the merchants open but surely this should not happen.
The thing is the kettle would have only been on for a minute and breakers tend not to trip until 1.5 times there rated value...which the kettle would have only just been over that, but then would take a certain amount of time before it trips anyway, which you would have to look at the graphs in the regs book to find out how long it would take...you will probably find it takes longer than boiling a kettle!
Check the time/current characteristics for a 6A MCB and you will see why. 3KW Kettles are normally only drawing current for a couple of minutes, for a full kettle. Half full of water, then even less time...
Next time you put the kettle on, clamp your ammeter on the cable at the MCB... All will become clear :)
funnily enough, just done that. clamp in main tail, current reading 2.4A. switrched on 3kW kettle, reading up to 10.8A. so 3kW my arse!
Glad I'm not the only one to have put the kettle on lol.
My 2.2Kw kettle pulls 2.3Kw (Got a keypad meter here which will give your KW load, load cost etc etc), got a voltage of 244v at the moment though so its about bang on.
It's a damn site more accurate than clamp metres.
Reply to 6 Amp RCBO 13 Amp load in the UK Electrical Forum area at ElectriciansForums.net
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...