Hello Everyone

Will be wanting a grid switch with 4xdp switches to control 4 spurs with a single socket on each. Ring main in and out plus 4 spurs of the switches equals 6 2.5mm cables. I've got a 4 module mk grid backbox - about 45mm depth I think.

Is it possible? I'm thinking the 4 spurs might just enter the bottom of the box and go straight into their respective switches but it might be hard to get all 6 earths terminated?
 
47mm back box and:

2273-208.jpg
 
Beginning of the summer tested ten houses for a housing association on a five year old estate. Eight out of the ten had open continuity faults on at least one conductor on the kitchen ring final circuit. Back to do remedials, first house found in 30 odd minutes at the four gang control grid. All bar one of the others at the same point. Half a day I had resolved all eight. Bad design? or the whole MK grid unit totally inadequate for a ring final using 2.5 solid conductors. Admittedly the links could have been stranded 2.5 but nevertheless.
 
The cpcs are not the problem I did as suggested in #6 by @Strima just chopped the lot and put in a Wago with a link to the grid. The whole lot were so badly connected.
 
Beginning of the summer tested ten houses for a housing association on a five year old estate. Eight out of the ten had open continuity faults on at least one conductor on the kitchen ring final circuit. Back to do remedials, first house found in 30 odd minutes at the four gang control grid. All bar one of the others at the same point. Half a day I had resolved all eight. Bad design? or the whole MK grid unit totally inadequate for a ring final using 2.5 solid conductors. Admittedly the links could have been stranded 2.5 but nevertheless.

I'm inclined to agree! I'm probably being naive, but wouldn't the customer have noticed if any of the conductors (apart from earth) was open ? I mean their fridge wouldn't be working....

Also, are you giving me a hint that using 2.5 stranded for the links between each switch might make it slightly easier?
 
I'm inclined to agree! I'm probably being naive, but wouldn't the customer have noticed if any of the conductors (apart from earth) was open ? I mean their fridge wouldn't be working....

Also, are you giving me a hint that using 2.5 stranded for the links between each switch might make it slightly easier?

A discontinuous ring connection at one terminal would not mean any power loss to any one grid switch.
 
I'm inclined to agree! I'm probably being naive, but wouldn't the customer have noticed if any of the conductors (apart from earth) was open ? I mean their fridge wouldn't be working....

Also, are you giving me a hint that using 2.5 stranded for the links between each switch might make it slightly easier?
Good point, most were cpc issues and a disconnected line or neutral will still allow the others to function as the one conductor was still in place.
Stranded conductors allow that bit more flexibility but I find with the MK grid terminals are far too shallow especially for solid 2.5. I expected they just popped out when the grid was screwed back.
 
A discontinuous ring connection at one terminal would not mean any power loss to any one grid switch.

Oh yes of course. Hence the ring. Thanks for your correction !

The pic in #6 is that an 8 way waygo? So could put all the earths in that with one going to the backbox?
 
...
Stranded conductors allow that bit more flexibility but I find with the MK grid terminals are far too shallow especially for solid 2.5. I expected they just popped out when the grid was screwed back.

DIYers get a bad press and many don't like all the regulation but my gosh. Surely whoever did that in a housing association must have been a professional electrician that should have had and used a multifunction tester (as I have). In fact I think you could diagnose that fault with a simple multimeter.

MAny thanks once again for all the advice and great tips.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
6 cables in a backbox?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
Deleted member 112675,
Last reply from
Deleted member 112675,
Replies
15
Views
2,186

Advert

Back
Top