Carrying out and EICR on large factory and they have welding plug into 63 amp commando sockets but are protected by 30 amp BS 88 fuses.
Now the regs states Socket outlets with a ratted current not exceeding 32 amp need RCD protection. 411.3.3 (i)
Because the Socket it 63 amp I say it does not need RCD protection because its the ratting of the socket that decides if an RCD is required ,not the over current protective device. So am not going to code this just put it as info on the observations.
Or would you guys Code it ?
Got me thinking though if you wanted to avoid fitting an RCD and don't what to do a risk assessment, just fit a 63 amp plug and socket and protected by a 16 amp MCB , Not sure how you would terminate the 1.5mm flex in the plug though
Now the regs states Socket outlets with a ratted current not exceeding 32 amp need RCD protection. 411.3.3 (i)
Because the Socket it 63 amp I say it does not need RCD protection because its the ratting of the socket that decides if an RCD is required ,not the over current protective device. So am not going to code this just put it as info on the observations.
Or would you guys Code it ?
Got me thinking though if you wanted to avoid fitting an RCD and don't what to do a risk assessment, just fit a 63 amp plug and socket and protected by a 16 amp MCB , Not sure how you would terminate the 1.5mm flex in the plug though