Hi all

This is a follow up from a previous thread I posted about 16mm tails.

Just had two electricians round to quote for a board change, they were both happy to do it with 16mm tails but the incoming earth is only 6mm they have advised me to get onto the electricity supplier and upgrade the earthing and wont do the board change until done. Internal bonding is also 6mm

Sounds right? (not that I don't have faith in the sparks just seeking thoughts on this)
 
Definitely a 6mm that's been confirmed funny thing is underneath next to this looks like a chopped earth cable which is much bigger
Yes, I'm rolling back on this.

Here is a 6mm² in relation to my 25mm² tails and 16mm² main earth.
[ElectriciansForums.net] 6mm incoming earth
 
It's the sort of situation that might result in a Catch 22 unless some common sense is applied.

When you go ahead with the fuse upgrade it is entirely possible that the DNO will demand an up to date electrical certificate for the property to show that everything is in place and suitable for 100A, before they do any work. So then you'd end up in a Chicken vs Egg situation.

In most cases (having carefully assessed the situation) I'd personally feel comfortable with doing as suggested, with 16mm earth from the new board to a block near to the main head (and likewise with 25mm tails to henley blocks connecting to the existing 16mm ).

That would be on the understanding that the earth was to be upgraded (or that the DNO would decide they were happy with existing) - as well testing the existing Ze (test of the level of the current earthing) and a quick check with the adiabatic. I'd upgrade main bonding to 10mm too where it was reasonably practicable to do so.
 

Reply to 6mm incoming earth in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
332
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
859
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
983

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top