6MM MAIN EARTH on a tt system with 100 ohm ze at db ,it runs under patio to rod .do i have to upgrade it as it means patio has to come up ? The electrode should be visible for inspection,which it wont be under the patio.However as you are only undertaking minor works as long as the electrode Ra is ok you could just note it on your MW cert...(or install another rod elsewhere??) old wylex 6 way rewireable fuse board protected by old crabtree 60amp elcb i have to add a spur for a stannah stair lift and upgrade the non existing bonding customer not happy where do i stand?An ELCB is no longer an acceptable means of earth fault protection,either upgrade to RCD,or fit an RCD purely for the circuit you are altering....either way you cant use an ELCB for EFP for your alteration. Your call on main bonding,it should be in place...but if you consider that lack of bonding does not affect the safety of your install you may decide to omit it and note the reason on your cert....that would be a last resort.