Hi,

Just a question, I know what I would do but wondering what others do.

7/.036 is the old imperial version of 4mm supposedly, do you put it on a 20A MCB or a 32A MCB ??

We are referring to a radial, not a ring.

Personally I put it on a 20A MCB, as looking at the old regs book, not that I have one, but one I found, it can only take 27A if I am correct.

I did a consumer unit change today, had an 8.5kW shower connect on a 7/.036 with 30A Fuse, never been a problem, but I have just disconnected it and put a warning on it etc, we had the conversation of rewiring it which could be done in about 2 hours with minimal effort and the customer didn't want it.

The customer has called me and said he has reconnected it, can't help some people, I did connect it and see how much it was pulling and it was 35.9A.

[ElectriciansForums.net] 7/.036 Cable
 
As Andy says , this should have been checked before specifying or changing the board , questions like this can't be asked after the work has been done ...
 
Last edited by a moderator:
I'll be honest it was partially an oversight on my part thinking it was 6mm when briefly looked, it was one of those jobs where I tested it first then changed all on the sand day which I don't usually do. But the customer wanted me to get on with it.

I have not been caught out like this before so am a big annoyed with myself to be honest, but anyway it's where we are, I had got the time today to change the cable as it could easily have been changed to the isolator where it had current 6mm to the shower.
 
To be honest you are a little bit buggered.
You've made a mistake and now the only way you can fix it is install a suitably sized cable on a 40A mcb.
Now if you're good with the bull**** you might get away with the customer paying for it, or maybe paying for materials only. Failing that you're going to have to take it on the chin and accept the cost.
Hopefully you allowed enough contingency in your price that it won't be an overall loss on this ine
 
To be honest you are a little bit buggered.
You've made a mistake and now the only way you can fix it is install a suitably sized cable on a 40A mcb.
Now if you're good with the bull**** you might get away with the customer paying for it, or maybe paying for materials only. Failing that you're going to have to take it on the chin and accept the cost.
Hopefully you allowed enough contingency in your price that it won't be an overall loss on this ine

I agree totally, it was my fault for not spotting it, i don't suppose I'm the first one. It was an easy mistake to make looking at the cable. I'm happy to change the cable for a new one for free other than parts which won't come to much.

Its to an easy run so it's not a major problem.

its had an 8.5kW shower running on it for nearly 10 years with a 30A fuse.

ill give the bloke a call and arrange to swap it.
 
Okay, so you changed the cu, oversight on your behalf with the under rated shower cable circuit, advised customer of the fact, you disconnect, he has re energized the circuit that has been insitu for 10 years, no thermal damage on cable?, IMO don't replace for free, else stick it on 20amp mcb when it goes pop down to the client to make the move.
 

Reply to 7/.036 Cable in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
184
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
562
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
761
  • Question
Its important to remember that a plug top fuse is just a rewireable fuse that's convenient to change and shouldn't be confused with a HRC fuse...
2
Replies
15
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top