uksparks
-
Hi,
Just a question, I know what I would do but wondering what others do.
7/.036 is the old imperial version of 4mm supposedly, do you put it on a 20A MCB or a 32A MCB ??
We are referring to a radial, not a ring.
Personally I put it on a 20A MCB, as looking at the old regs book, not that I have one, but one I found, it can only take 27A if I am correct.
I did a consumer unit change today, had an 8.5kW shower connect on a 7/.036 with 30A Fuse, never been a problem, but I have just disconnected it and put a warning on it etc, we had the conversation of rewiring it which could be done in about 2 hours with minimal effort and the customer didn't want it.
The customer has called me and said he has reconnected it, can't help some people, I did connect it and see how much it was pulling and it was 35.9A.
Just a question, I know what I would do but wondering what others do.
7/.036 is the old imperial version of 4mm supposedly, do you put it on a 20A MCB or a 32A MCB ??
We are referring to a radial, not a ring.
Personally I put it on a 20A MCB, as looking at the old regs book, not that I have one, but one I found, it can only take 27A if I am correct.
I did a consumer unit change today, had an 8.5kW shower connect on a 7/.036 with 30A Fuse, never been a problem, but I have just disconnected it and put a warning on it etc, we had the conversation of rewiring it which could be done in about 2 hours with minimal effort and the customer didn't want it.
The customer has called me and said he has reconnected it, can't help some people, I did connect it and see how much it was pulling and it was 35.9A.