Greetings.
Just had the upstairs shower die, water is leaking all over the place and it is highly dangerous.
We have a 6mm cable fused at 32A at the CU with no RCD.
My father is a real difficult old bloke of 85 years and whenever I try to tell him about RCD's and new fuse boards he gets really angry like I am trying to cheat him out of money.
All I can see available are 7.5 KW showers these days, can't seem to find a 7KW one.
I think I am right in assuming a 7.5KW shower should be fused at 40A.
Do you think the 6mm cable will be allright as it is with no need to fit a new cable?
It seems really borderline to me, cable is surface clipped up to the loft then it drops down to behind the upstairs shower. Cable run is about 15 metres.
An RCD in its own enclosure seems the only way to do this as a new fuse board is out of the question.
Any opinions?
Thanks.
 
Last edited:
Garro do a changeover device in its own enclosure and you can set priority to either side, might be worth a look
Thanks, this is the same one as the link sent to me by Zerax. I'm guessing that the same principle but not automatic, would be to use a 40 or 32 amp normally closed contactor. I can find a 40a NO contactor but not a 40a or 32a NC contactor.
 
Ok, found a cheaper 2 pole one at ÂŁ35. Just wondering if it would pass an EICR as you would need a 1.5mm cable running back from the isolating switch for the shower to the consumer unit wired into the contactor.
 

Reply to 7.5KW shower with 6mm cable in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
767
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top