Hi i've put in a new ring with 3 sockets and 3 fcu but when i do the ir test i only getting

L-E 74
L-N >200
N-E 134

i was going to brake it half way then test then so on

any tips
 
70 Mohms...!....not exactly REALLY low, Have you plastered any boxes in or installed on damp walls?,if so condensation in the backbox might be the cause.Otherwise I wouldnt worry about it,as long as all your other readings measure up it's well over the minimum acceptable reading.
 
Hi i have labc to site on monday

When i take all the sockets and fcu's off i was getting >200 ohms and i test all the sockets all ok but when connected getting all kind of readings as low as 30 megger ohms
if i leave the tester lock on will claim to 160
 
Wouldnt worry too much about it its that time of the year now nothing seems to dry out very quickly bet you would get a much higher reading in july only needs a little pressure on the back boxes when screwed back to get a lower reading also make sure everything is disconnected even diodes on fused spurs
 

Reply to 70m ohms on ir test on a new ring ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
864

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332
  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
855

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top