I'm not sure what your assumptions about the installation surroundings have to do with cable size. My comment you quoted related purely to cable size.
I'm also not sure why you have assumed the OCPD size, it's not been mentioned.
I was also referring to cable size and the fact that the OCPD size was not stated did concern me. The ring to the junction boxes is wired with 1.5 mm2 (see original post) and I would expect that to be protected by a 10A MCB - maybe even a 16A MCB, whereas Table 4F3A states that any installation circuit with 0.75 main conductors (phase and neutral) must be protected by a maximum 6A MCB (or fuse) and 0.5mm2 cable by a 3A device.
I was surprised this had not been mentioned by anyone else (unless I missed it), and several people said they use 0.75 mm2 for downlighters. The OnSite Guide only gives tables down to 1mm2. However BS7671 does allow thinner wires if protected by a suitable over-current device. The ratings are conservative and a 10A MCB would possibly be adequate to avoid over-heating due to a fault, but we are required to work to BS7671, and that states 6A max.
If you had mentioned the 6A MCB requirement, I would not have responded. I read your comment as "it is of no concern".
Well, sorry, but it is if he is to comply with the wiring regulations. The only other way would be to provide a local lower-value (5A or 6A) SFC for the downlighter circuit, wall mounted to be easily accessible.
Maybe I am mis-understanding something?