8.5 Kw shower on 6mm tripping MCB | Page 2 | on ElectriciansForums

Discuss 8.5 Kw shower on 6mm tripping MCB in the Australia area at ElectriciansForums.net

O

olsonn

Went to a job today where a lovely new bathroom has just been fitted upstairs with a new 8.5 Kw shower replacing a 7.2kw one. After a few minutes in the shower the MCB trips. The shower was fully turned up and when I asked the customer they said that they always ran it like this. On inspecting the cable size it was 6mm. The cable is run up an internal concrete wall and appears to have been plastered in and not run in conduit The run is about 12 metres. It also runs through insulation in the loft As a matter of course I would run this size shower in 10mm. It is possible to run a replacement 10 mm cable up from the CU using trunking, but the cable from the switch which is also in 6mm and about 1.5 metres long, is buried behind a lovely expensive tiled wall and doesnt want to come out. Would it be acceptable to leave this short run in 6mm or should I tell the customer that we have to remove the tiles and replace the cable.
 
i suggested moving the insulation away from the cable. OK. brb give guidance on derating where necessary, due to insulation, but at the bottom of table4d5, page 282, read the note.
 
Is this for real?

If an 8.5 shower is tripping a 40A mcb, then chances are it's a faulty mcb. But check the shower current draw in case it's faulty (or it's not an 8.5, perhaps).

Nothing wrong with 6mm on 40A as long as it's clipped direct. just lift the cable out of the insulation and clip it to the woodwork. Extend it if necessary. Use a couple of lengths of 4 inch waste pipe to keep an air space around the cable where it must pass through the insulation layer. No need to spend ÂŁÂŁÂŁs on 10mm.

my thoughts exactly.
 
Just re-read this and IMO it is the cable that is the problem as in it is now under size for the 8500kW new shower due to it being run under that insulation. It's all ok when it starts off but as the cable warms up it can't dissipate the heat, resistance goes up current drawn increases etc. I'm looking at Table 4D5 which suggests 6mm2 sq, Ref Method 100# is only good for 34A if under 100mm of insulation and only 27A under more than 100mm.

I've had a beer so........daft idea maybe but how much room do have above the ceiling in the bathroom? You couldn't get in there with a 1m long SDS and drill a new hole down to the shower could you? I said it was mad! What's behind the wall? Come down the other side? Sorry, its the Amstel talking!

i always thought that increased resistance meant lower current. i agree that problems will arise if cable overheats, but 8.5kw ( manufacturers optimistic rating ) is only 35A. get the candy floss away and 6mm is good for 45A.
 
i think a lot of this 10mm nonsense for showers over 8KW (or 8.5, can't quite remember) came during the early years of the 16th whereby the IEE were worried about volt drop. this advice was amended as long as the total cable length didn't exceed 20meters. (that's 22 yards to those of us who still speak english)
 

Reply to 8.5 Kw shower on 6mm tripping MCB in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
312
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
941

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top